manual self test in PCPE causes computer to crash

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • manual self test in PCPE causes computer to crash
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

0 Likes
7
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

manual self test in PCPE causes computer to crash

I have a Dell computer running Windows 7
I have a APC Back-UPS ES 750.
I down loaded PCPE v3.0 for windows 7
when I execute the manual self test through the PCPE interface the computer crashes.
No log events are generated.
Do I have a bad UPS?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

We've seen issues like this as well on customers that were using BackUPS on Dell XPS Studios. The computer does not like the step sine wave the UPS generates when running On Battery. I apologize for the inconvenience this has caused you, have you contacted our APC Technical Support Team regarding this issue?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

yes. I sent an e-mail because it was Sunday, Feb 13th and chat was not available. There has been no response fro APC.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

I apologize for the inconvenience.

Our Phone Technical Support team has received these kind of issues as well. An issue that I have seen so far is the transfer time that it takes for the UPS to switch from Online to On Battery. Our BackUPS has a transfer time of 6-8ms, certain power supplies doesn't like or requires a lesser/shorter transfer time.

Here is a helpful kbase that talks about the reasons why would a certain load reboot or turn off.
[Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots.|http://nam-en.apc.com/app/answers/detail/a_id/20/kw/backups%20reboot]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

What is the exact model number of your Dell PC?

Also, if you unplug the UPS from the wall outlet or let's say it runs on battery does it causes the PC to crash as well? Can you tell us as well if the UPS has turned off when it crashed your PC or did the it remained on and completed the self test?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

My Dell computer is Studio XPS Desktop 435T/9000
The Self test did not complete.
I did not unplug the UPS prior to or during the self test.
The UPS did not turn-off during the self test.

I have not tried to unlug the UPS to see if the computer stays up.

Message was edited by: michael_ackleson@sbcglobal.net

Message was edited by: michael_ackleson@sbcglobal.net

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

While the PC and UPS are both on, can you unplug the UPS from the wall outlet and check if the UPS will be able to support the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:51 AM

I unplugged the UPS from the wall and the computer shutdown instantly.
back when I had powerchute installed and the data cable hooked up it showed that the battery had enough capacity to maintain the load for 10 minutes. It did not hold for 1 second.

I am taking the unit back to Best Buy and get a different brand of UPS. Not because this unit was bad. That happens. The reason I am moving away from APC is I have been waiting for more than a week for a reply from APC product support. If they do not care enough to acknowledge my request for assistance, then it is time for me to move on. I have three other APC units in my home that are working well. I do not plan to buy another one after this experience.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

0 Likes
0
1058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

We've seen issues like this as well on customers that were using BackUPS on Dell XPS Studios. The computer does not like the step sine wave the UPS generates when running On Battery. I apologize for the inconvenience this has caused you, have you contacted our APC Technical Support Team regarding this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of