84244members
353343posts
fault light on SURTD5000XLI
kumar_apc
601
This was originally posted on APC forums on 11/10/2014
Hi
I am repairing a SURTD5000XLI ups , the ups gives the following error light Fault code:
1
1
These lights shows on the right hand side.
What could be the cause of the problem?
Re: fault light on SURTD5000XLI
This reply was originally posted by Angela on APC forums on 11/10/2014
I don't see this as an available or possible code..
zejulio_apc
This was originally posted on APC forums on 2/16/2016
I have the exact issue.
Did you fixed it?
Once I had access to webpage, now I do not have anymore with new batteries...
It said that was ADC fault, and AC mains wore more than 400VAC, even with AC not connected...
7 Replies 7
kumar_apc
This was originally posted on APC forums on 11/11/2014
Hi
I have taken a picture of the error code if it will be of assistance.
This reply was originally posted by Angela on APC forums on 11/11/2014
Hmm, ok. Thanks. Let me investigate in the next day and get back to you. It is a holiday here today so I will be back tomorrow.
This reply was originally posted by Angela on APC forums on 11/13/2014
Thank you for the picture.
As I mentioned, I looked into it, and this is an ADC failure, or Analog to Digital Converter failure. As told to me by our EMEA support team for your area, we do not support such repair on end user level and if you are a certified service partner or bring it to one, they have access to documentation telling what the fault is and how to fix it.
kumar_apc
This was originally posted on APC forums on 11/17/2014
Hi Angela
The ups SURTD5000XLI i am servicing is not switching on, only when i
swap the logic board it switches on , where on the faulty logic board can I
look to solve the issue?
I have attached a picture of the logic board.
Umar
This reply was originally posted by Angela on APC forums on 11/17/2014
Hi Umar - I don't know the information you're asking for (because we don't service them here in NAM, only replace) but you are trying to service this if you're looking at the logic board and have removed it already. The only advice I can offer is to seek out a service partner in your area to see if they know the answer to the question. If anyone else wants to help and reply, it will be at everyone's own risk as I cannot condone working on this if you're not a certified service partner.
zejulio_apc
Did you fixed it?