Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Wiring a Smart-UPS RT 5000 to a distribution panel to supply 120v to the room

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Wiring a Smart-UPS RT 5000 to a distribution panel to supply 120v to the room
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mrabe_apc
Crewman mrabe_apc
Crewman

Posted: ‎2021-06-29 06:12 AM

0 Likes
3
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 06:12 AM

Wiring a Smart-UPS RT 5000 to a distribution panel to supply 120v to the room

This was originally posted on APC forums on 6/25/2013



We have an office that has a Smart-UPS 5000 (SURT5000XL) with a step down isolation transformer (SURT003) feeding a distribution panel. The panel then supplies 120v to the outlets in the room. I came across this office because we were having major problems with our equipment each time there was a power disturbance. We found that the electrican was not using the step down transformer to feed the panel so there was not a proper neutral. We are now using the the isolation transformer inline and using the L14-30 output on it to connect it to the panel.

A new electrician was used to put the transformer inline but after the last one I wanted to double check his work.

1. Should the neutral bus on the panel should be floating or if it can be bonded with the panel?

2. Does the attached diagram show how the system should be installed?

Thank you,

David

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • distribution
  • distribution_panel
  • electrical_question
  • installation
  • smart-ups
  • smart-ups_rt
  • wiring
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:12 AM

0 Likes
0
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 06:12 AM

This reply was originally posted by Jonathan on APC forums on 6/25/2013


Hi mrabe,

I hope this can help you out.

In response to your second question.  As per NEC rules, it is illegal to use a plug-in and then wire that up to a panel.   With regards to your first question - when using a 4-wire transformer output, you would treat it the same as utility power.  Neutral and Ground can be bonded in the panel if that is how the panel is designed.  You must use the Neutral from the transformer in the panel.  The AP9628 is best, but it only gives you a single leg of 120v.  If you only need 120v loads/output, it will work fine.  If you truly need a 4-wire hardwire output, the proper transformer would be the APTF10kW01.  Keep in mind that the APTF10kW01 is a 10kVA unit, if you will be using this on your 5kVA you will only be limited to 5kVA on the transformer.

The other (better) option would be to just use a spiltphase 5kVA unit with a hardwire kit, SURTD5000RMXLP3U with the SURT018.

See Answer In Context

Reply
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:12 AM

0 Likes
0
367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 06:12 AM

This reply was originally posted by Jonathan on APC forums on 6/25/2013


Hi mrabe,

I hope this can help you out.

In response to your second question.  As per NEC rules, it is illegal to use a plug-in and then wire that up to a panel.   With regards to your first question - when using a 4-wire transformer output, you would treat it the same as utility power.  Neutral and Ground can be bonded in the panel if that is how the panel is designed.  You must use the Neutral from the transformer in the panel.  The AP9628 is best, but it only gives you a single leg of 120v.  If you only need 120v loads/output, it will work fine.  If you truly need a 4-wire hardwire output, the proper transformer would be the APTF10kW01.  Keep in mind that the APTF10kW01 is a 10kVA unit, if you will be using this on your 5kVA you will only be limited to 5kVA on the transformer.

The other (better) option would be to just use a spiltphase 5kVA unit with a hardwire kit, SURTD5000RMXLP3U with the SURT018.

Reply
mrabe_apc
Crewman mrabe_apc
Crewman

Posted: ‎2021-06-29 06:12 AM

0 Likes
0
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 06:12 AM

This was originally posted on APC forums on 6/26/2013


Thanks Jon, exactly the information I needed.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:12 AM

0 Likes
0
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 06:12 AM

This reply was originally posted by Jonathan on APC forums on 6/26/2013


You're welcome, glad to help.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.