Posted: 2023-03-10 08:42 PM . Last Modified: 2023-03-10 08:47 PM
Hm, I used to have an account at the APC.com forums, but it seems to have been deleted. (Last login around 2018)
I started a small project for myself to upgrade my older APC Smart-UPS 1500 (SUA1500i) from AGM SLA batteries to LiFePO4 batteries with advanced BMS. Normally UPS units that are designed to work with SLA batteries are not compatible with LiFePO4 batteries, some battery manufacturers have designed an advanced BMS (Battery management system) that allow LiFePO4 batteries to be used in any application where SLA batteries are normally used.
I used 12v 30Ah PowerBrick+ batteries from PowerTech systems. These are fairly expensive but they should last a lot longer than traditional SLA batteries. These batteries can have 3000 cycles at 100% DoD or 4500 cycles at 80% DoD.
This guide should work for any Smart-UPS that uses the same batteries and same connector (APC RBC7)
https://youtu.be/tSfOPcbxAqk
This video is not sponsored. I bought the batteries myself.
Using LiFePO4 batteries in APC units made for SLA batteries is NOT supported by APC.
See video description for important information.
Posted: 4 weeks ago
I am very interested in these LiFePO4 substitution projects, because lead-acid is just a horrible technology, and APC's battery monitoring and failure detection has been technically deficient forever. A LiFePO4 BMS substitution may not be built to APC's intended usage, but their "intended usage" is terrible also.
At this very moment I have an APC 1500va LED with a dead APC RBC7 battery pack in a small server room, but which the UPS believes there are no problems with the RBC7. If I run a manual self-test it drops the load and the Dell PowerEdge server R630 suddenly turns off!
Nice work there APC, I thought you fixed this faulty technical implementation and moved over to using resistive simulation loads for self testing, when your products changed from beige to black.
So anyway, a specific problem that you may experience with your LiFePO4 is that the onboard BMS needs to pretend it is a lead-acid battery, and slope the output voltage up and down as the LiFePO4 discharges.
You do NOT want a BMS that outputs a steady "full-charge" voltage of 13.6v until the lithium battery is discharged, at which point the BMS suddenly turns off.
This defeats the UPS from being able to determine the state of discharge by monitoring the battery voltage as it discharges. The UPS will have no way of knowing when to enter the "low-battery" phase and send the alert signal that the server should start the automatic shutdown or suspend procedure, to prepare for loss of power.
Ideally the BMS output voltage should slope down to approximate the declining state of charge of a lead-acid battery as the LiFePO4 discharges.
Also it may potentially be better to use a 24 volt LiFePO4 with the same approximate size as the two 18ah lead-acid batteries next to each other. This allows for bigger cooling heatsinks in the combined BMS, fewer BMS components to fail, and also larger lithium cells in the unpartitioned bottom casing.
Posted: 4 weeks ago
The usage of a single 24V LiFePO4 battery is actually quite a nice idea. It may help to prevent any balance issues, if any. I just took 2x 12V replacements to stay the nearest to what the APC expects.
PowerTech Systems also has a 24v variant. The connectors will be at a different place and you need to check if the physical dimensions are right for this unit.
https://www.powertechsystems.eu/wp-content/uploads/specs/PowerBrick_PRO+_24V_32Ah_Lithium-Ion_batter...
Posted: 4 weeks ago
Also there is another problem with these LiFePO4 substitutions. You need to carefully examine the specifications for the substitute battery to make sure the onboard BMS can actually output the full capacity of the original lead-acid battery pack, for the maximum load watts for the UPS.
In the UPS I am discussing here: APC SMT1500 - Maximum load 1000 watts, 1500 VA
Lead acid battery, general characteristics:
As any kind of battery discharges, gradually the amperage increases:
The PowerBrick 12v / 30ah Standard will not work for this, but the PowerBrick Pro+ can do it... nearly.
(Whether the Pro+ actually drops to 21.0v at end of lithium discharge, I don't know.)
Standard:
Pro+:
Meanwhile this lower-quality 12v LiFePO4 of a similar physical size from ExpertPower is pretty much useless:
https://www.expertpower.us/products/ep1220-20ah
ExpertPower EP1220
You would have to use two of the much larger ExpertPower battery that won't physically fit in the APC 1500VA battery compartment.
https://www.expertpower.us/products/ep1250-50ah
ExpertPower EP1250
For people that are not buying quality LiFEPO4 with a built-in drop-in 12v/24v BMS, there is the potential to be severely disappointed if their cheap PongHuan Fzdagbu Amazon battery for US $50 fails at the worst possible moment because it can't handle more that 20% the UPS maximum rated load capacity... lol