Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82519members
350119posts

UPS turns itself off every 4-5 days

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

jeremyprosolit
Cadet
0 Likes
1
206

UPS turns itself off every 4-5 days

Hello everyone,

 

We have a Smart-Ups X 1000 and every 4-5 days the UPS turns itself off. It must therefore be turned on manually via the on/off button. 

In the log we can see the following messages :

 

2022-06-01 - 22:29:42 - On Line (Green Mode) - Exited

2022-06-01 - 22:29:42 - PowerChute Agent outlet turning off (by external entity)

2022-06-01 - 22:29:42 - Monitoring Stopped

 

The UPS is connected via USB to an HP Proliant server with Windows server 2022.

 

There is never anyone in the offices when this is happening.

 

Has anyone had this problem before?

Thank you in advance, have a nice day.

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
136

Re: UPS turns itself off every 4-5 days

@jeremyprosolit 

 

I recommend you turn off green mode. From the LCD panel of the UPS go to Configuration - Green Mode - Disable. The check the Event Log to see if the UPS recorded outlet group off at the time PowerChute recorded it.

 

 