UPS: The external DC disconnect switch is open

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Mgregory2K_apc
Ensign
Ensign
0 Likes
1
192

UPS: The external DC disconnect switch is open

This was originally posted on APC forums on 12/15/2009


Can anyone tell me what this means really quick? I got the alert emailed out this past weekend and I thought this was a physical switch, but nobody was in the building.

The "no longer open" alert came in about 1 minute later so nothing was harmed, but I can't find any info on the specific alert.

Thanks in advance


Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
192

Re: UPS: The external DC disconnect switch is open

This was originally posted on APC forums on 12/15/2009


Yes, this is a physical DC battery breaker. You can try cycling the breaker to make sure it's back in a solid "ON" position, and verify via the switches/breakers in your PowerView display. Potential faults could be a faulty contact or external switchgear card. If you continue to experience the fault or need more clarification it would be best to call into our three-phase support/Symmetra PX support team at 1-800-800-4272.

See Answer In Context

1 Reply 1
Erasmus_apc
Sisko
Sisko
0 Likes
0
193

Re: UPS: The external DC disconnect switch is open

This was originally posted on APC forums on 12/15/2009


Yes, this is a physical DC battery breaker. You can try cycling the breaker to make sure it's back in a solid "ON" position, and verify via the switches/breakers in your PowerView display. Potential faults could be a faulty contact or external switchgear card. If you continue to experience the fault or need more clarification it would be best to call into our three-phase support/Symmetra PX support team at 1-800-800-4272.