UPS SURT10000XLI doesn't work!

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
kiba_apc
Cadet
0 Likes
1
273

UPS SURT10000XLI doesn't work!

This was originally posted on APC forums on 10/6/2016


I replaced the batteries, after that, The UPS shows me the following message:

Errot

Please I don't know What Happened!

Attachments

Accepted Solutions
MarkC_apc
Commander
Commander
0 Likes
0
273

Re: UPS SURT10000XLI doesn't work!

This was originally posted on APC forums on 10/6/2016


The red LED indicates an internal fault in the UPS.  The third from the top green LED indicates that the problem is in the power factor correction portion of the UPS.  This is not user fixable.  If under warranty, contact Schneider.  

However, since it appears to be related to a battery replacement, you should ensure that the four battery cages are in good condition, fully charged and properly connected.  

See Answer In Context

1 Reply 1
MarkC_apc
Commander
Commander
0 Likes
0
274

Re: UPS SURT10000XLI doesn't work!

This was originally posted on APC forums on 10/6/2016


The red LED indicates an internal fault in the UPS.  The third from the top green LED indicates that the problem is in the power factor correction portion of the UPS.  This is not user fixable.  If under warranty, contact Schneider.  

However, since it appears to be related to a battery replacement, you should ensure that the four battery cages are in good condition, fully charged and properly connected.