Trying to reset the parameter "Battery Constant" for an SU2200NET

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Trying to reset the parameter "Battery Constant" for an SU2200NET
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

0 Likes
6
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

Trying to reset the parameter "Battery Constant" for an SU2200NET

Hi and I hope someone can provide me with some tips on how to proceed:

I am trying to reset the battery constant for my 1999 vintage SU2200NET. I contacted APC tech support via a "chat" instance and was provide the value of hex "AF" as the constant for this UPS.

Using the correct serial cable, I "hyperterm'd" into the unit as follows:

1. Shift-Y. UPS responded with "SM".
2. 0 (zero). UPS responded with "8D". This is the current value of the battery constant.
3. Attempted to change the value using the + (plus) and - (minus) keys.
note: Instead of incrementing or decrementing the value, each time I pressed the key I received the "NO".
4. Shift-R. UPS responded with "BYE".

Does anyone know what the response "NO" means and if there is any way to cause EEPROM/NVRAM to begin to accept the requested change to the battery constant?

I also have an AP9630 (which WAS NOT installed while talking to the UPS via the serial port) but I don't think there is any way to change the battery constant via the NMC.

Any help would be greatly appreciated!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

๐Ÿ˜‰

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

i think you're missing a step. here are the instructions i have. try this in place of your step 2. press 1 and then about 4 seconds later, press 1 again (should get "PROG"). THEN press 0 and record the value.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

Right you are! I suspected it was a "cockpit" issue. I'll redo it and let you know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

๐Ÿ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:41 AM

I sure am glad we have you here to shepherd us along toward APC nirvana!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:40 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:40 AM

Hello Angela,

I am hoping you can help with this one too. I have a very old SMART-UPS 1250 and just replaced the batteries in it. The run time of 23 minutes did not change after replacement and seems low to me. I am trying to reset the battery constant but it seems this model is even older and does not respond to the 1 1 command to enter prog mode.

I opened hyperterminal.

Sent Y

Received SM

Sent 0 (zero)

Received 4E

Pressed 1 1 (tried numerous times.)

Received nothing at all.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:40 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 11:38 PM . Last Modified: โ€Ž2024-03-11 04:40 AM

If the UPS predicts 23 minutes of runtime, then you can do a runtime calibration, either via PowerChute or a network management card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of