Thremal Dissipation versus calculated BTU/hrs

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
TRC_Eng_apc
Cadet
0 Likes
1
91

Thremal Dissipation versus calculated BTU/hrs

This was originally posted on APC forums on 11/29/2010


Symmetra LX 8kVA - How is the Online Thermal Dissipation 4995.00 BTU/hr calaculated when @ 6400 Watts it is 21850 BTU/hr


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
91

Re: Thremal Dissipation versus calculated BTU/hrs

This reply was originally posted by Matt on APC forums on 11/29/2010


Hi Dominick,

The Symmetra LX 8kVA chassis, when fully loaded at 6400W/8kVA has an online thermal dissipation of 3485BTU/hr. See [online specs|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SYA8K8P].

If the UPS is powering a 6400W load, then the 6400W is not escaping as thermal energy like a huge toaster oven -- it's doing work to drive the downstream electronics.

Any thermal dissipation is a result of the way the UPS produces its output, including any inefficiencies in its design. The 3485BTU/hr spec is for an 8kVA chassis with 3 power modules operating at 100% load (6400W / 8kVA) and already fully charged. If this same system is rapidly charging the batteries the thermal dissipation is 6472BTU/hr.

Those two values would be the "worst-case scenario" specs for normal online (charged) and online (actively re-charging) modes for that chassis. If you run the UPS at less than its maximum load capacity, the thermal dissipation would obviously be less.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
92

Re: Thremal Dissipation versus calculated BTU/hrs

This reply was originally posted by Matt on APC forums on 11/29/2010


Hi Dominick,

The Symmetra LX 8kVA chassis, when fully loaded at 6400W/8kVA has an online thermal dissipation of 3485BTU/hr. See [online specs|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SYA8K8P].

If the UPS is powering a 6400W load, then the 6400W is not escaping as thermal energy like a huge toaster oven -- it's doing work to drive the downstream electronics.

Any thermal dissipation is a result of the way the UPS produces its output, including any inefficiencies in its design. The 3485BTU/hr spec is for an 8kVA chassis with 3 power modules operating at 100% load (6400W / 8kVA) and already fully charged. If this same system is rapidly charging the batteries the thermal dissipation is 6472BTU/hr.

Those two values would be the "worst-case scenario" specs for normal online (charged) and online (actively re-charging) modes for that chassis. If you run the UPS at less than its maximum load capacity, the thermal dissipation would obviously be less.