Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82628members
350277posts

The battery power is too low to support the load issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
raz23_apc
Cadet
0 Likes
1
220

The battery power is too low to support the load issue

This was originally posted on APC forums on 6/11/2014


Hello,

           I've recently installed a UPS in the same room with two other UPS's. We installed a new outlet for the new one and after we plugged it in, one of our other UPS's started spitting out errors that the battery power is too low to support the load issue. Then about a minute later, that a discharged battery condition no long exists. In the UPS that's spitting out the errors, it's a Smart-UPS 5000 RM DL4 and we just replaced the batteries in it last month with new ones. I was looking at the data logs and the %Wout went from a constant below 20 to above 22 after we plugged in the new UPS. The other UPS in the room is not spitting out any errors though after the new one was plugged in. I'm not too sure what's going on. I appreciate any help in solving this issue.

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
220

Re: The battery power is too low to support the load issue

This reply was originally posted by Angela on APC forums on 6/11/2014


Are you using a Network Management Card or PowerChute Business Edition? Essentially, this may just be a configuration/reporting issue is my first thought.

We need to know the UPS reported runtime and also what the "low battery signaling time" or "low battery duration" time is (depending on if using a Network Management Card or PCBE it will be worded differently).

I have a feeling that the reported runtime is low and the system may need to be calibrated to update the runtime. If you're reported runtime falls within two minutes of your low battery time, the UPS reports this type of thing to tell you that the battery in the UPS does not have much capacity whether on battery or not. It can be erroneous if the UPS is not reporting the correct amount of runtime.

Based on what you describe, you may have this symptom too -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

It could just be a coincidence that it happened when you connected another UPS. If you do have a Network Management Card, I am interested in event.txt, data.txt and config.ini as well (Instructions are here on downloading -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
221

Re: The battery power is too low to support the load issue

This reply was originally posted by Angela on APC forums on 6/11/2014


Are you using a Network Management Card or PowerChute Business Edition? Essentially, this may just be a configuration/reporting issue is my first thought.

We need to know the UPS reported runtime and also what the "low battery signaling time" or "low battery duration" time is (depending on if using a Network Management Card or PCBE it will be worded differently).

I have a feeling that the reported runtime is low and the system may need to be calibrated to update the runtime. If you're reported runtime falls within two minutes of your low battery time, the UPS reports this type of thing to tell you that the battery in the UPS does not have much capacity whether on battery or not. It can be erroneous if the UPS is not reporting the correct amount of runtime.

Based on what you describe, you may have this symptom too -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

It could just be a coincidence that it happened when you connected another UPS. If you do have a Network Management Card, I am interested in event.txt, data.txt and config.ini as well (Instructions are here on downloading -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...