The battery is not installed properly (AP9630)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The battery is not installed properly (AP9630)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 03:00 AM

0 Likes
3
3802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 03:00 AM

The battery is not installed properly (AP9630)

Hi,

I have a Model Number:AP9630, Serial Number: ZA1239008017; Application Module: sumx v5.1.7

 I've configured alerts on it and since 4 weeks I receive this kind of alert :

Critical - UPS: The battery is not installed properly.

and then about 1-2 minutes later a receive this one :

Informational - UPS: The battery is now installed.

Sometimes turns itself off. It has already happened twice. 

Does it help if I update firmware? Please give me a link for this.
I thank you in advance for your help.

LOG:

 03/28/2017 11:21:58 UPS: The battery is not installed properly.
 03/28/2017 11:21:38 UPS: The battery is now installed.
 03/28/2017 11:12:05 UPS: The battery is not installed properly.
 03/28/2017 11:11:44 UPS: The battery is now installed.
 03/28/2017 11:07:59 UPS: The battery is not installed properly.
 03/28/2017 11:07:39 UPS: The battery is now installed.
 03/28/2017 10:46:49 UPS: The battery is not installed properly.
 03/28/2017 10:46:29 UPS: The battery is now installed.
 03/28/2017 10:42:43 UPS: The battery is not installed properly.
 03/28/2017 10:42:03 UPS: The battery is now installed.
 03/25/2017 00:21:01 UPS: The battery is not installed properly.
 03/25/2017 00:20:41 UPS: The battery is now installed.

etc.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
3802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Hi Vitaly - based on the fact you said the UPS has turned off once in a while, I tend to believe the battery in the UPS is really failing. Sometimes the condition of "replace battery" presents itself like this depending on how the battery has failed. My guess is that the battery voltage may be fluctuating and when it drops below a certain point, the UPS cannot detect the battery anymore. And the voltage must be fluctuating quickly back and forth to see the behavior you saw. 

You can check the data log for battery voltage. So far we have only see your event log.

Either way, my gut feeling is that you should plan to purchase a replacement battery for your UPS as soon as you can. The serial number also indicates it was manufactured in early 2013 so assuming you haven't replaced the battery yet, it seems normal that it is about 4 years old now and needs a new one.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
3802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Hi,

You can update the firmware of the card but the issue may be communication within the UPS itself. Here is a link the the software firmware download site where you can download the latest firmware for the network card.

http://www.apc.com/de/de/tools/download/index.cfm?ISOCountryCode=de

You should select Firmware Upgrade - UPS Network Management Card from the drop down menu and then select SFSUMX646

What is the exact model number of the UPS? You will find that information on the bar code stick on the back or bottom of the UPS.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
3802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

I have a Model 3000RMI2U.

Upgrade was successful

So far I can not find any error.

I hope this helped. I wait until tomorrow, if this error message shows.

I sign up tomorrow, what is written in log file.

Danke )

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

0 Likes
0
3803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:57 AM . Last Modified: ‎2024-03-18 02:59 AM

Hi Vitaly - based on the fact you said the UPS has turned off once in a while, I tend to believe the battery in the UPS is really failing. Sometimes the condition of "replace battery" presents itself like this depending on how the battery has failed. My guess is that the battery voltage may be fluctuating and when it drops below a certain point, the UPS cannot detect the battery anymore. And the voltage must be fluctuating quickly back and forth to see the behavior you saw. 

You can check the data log for battery voltage. So far we have only see your event log.

Either way, my gut feeling is that you should plan to purchase a replacement battery for your UPS as soon as you can. The serial number also indicates it was manufactured in early 2013 so assuming you haven't replaced the battery yet, it seems normal that it is about 4 years old now and needs a new one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of