82687members
350407posts
Symmetra Power Array XR Frame not sensed
brobins3d_apc
705
This was originally posted on APC forums on 10/22/2008
Now that our Symmetra purchased via auction is running, we turn our attention to the XR frame.
We don't get the green light in the back, nor the frame number in the front. The frame communication cable didn't come with the unit, so I tried a phone handset cable. Would this work or does it require a specially wired cable?
Is the XR frame like the power array logic where it would require at least one good battery for things to be recognized?
Bill
Tags (3)
Re: Symmetra Power Array XR Frame not sensed
This reply was originally posted by Matt on APC forums on 11/5/2008
Keep in mind that while it is not recommended to run the Symmetra Extended Runtime cabinet without its built-in communications, the UPS can and will maintain the batteries inside the XR frame.
Without communication between the XR frame and Main Intelligence Module, you will not have any intelligent battery management. The UPS will not know if there are bad batteries installed in the XR frame. Manual inspection/testing/rotation of the SYBATT modules would be required.
Also, with no communication to the XR frame, the UPS will estimate runtime based on only the batteries it can "see" and "count". While the UPS is online, the UPS uses a complex algorithm including the logical battery count to estimate runtime.
However, within 60 seconds of the UPS going on-battery for any reason, the UPS throws away that previous estimate and recalculates runtime based on the actual rate of discharge of the entire battery system. It does not need communication to XR cabinets to accurately calculate runtime while it is operating on battery. As long as the XR cabinet it properly connected via the big DC cable to the main Symmetra tower, those batteries are available to the Power Modules and will be used to power the load.
I recommend correcting the communication problem, likely SYXRCC related, so that the UPS can intelligently manage those additional batteries and warn you if there are any problems.
18 Replies 18
brobins3d_apc
I don't see any microlatch unless it is located inside the jack itself.
This reply was originally posted by Angela on APC forums on 10/22/2008
ok, check your email.
also, if the cable doesnt work, it will probably be a SYXRCC problem.
Sisko
Sisko
The symmetra XR communication cable should be a straight-through RJ9. This would be similar the handset cable, yes. What are the model numbers on your Symmetra frame and the XR frame itself?
brobins3d_apc
They're the tall beige cabinets. I believe it's a SY16EX and a SYBT12.
Sisko
Sisko
Ok, after double-checking on the particular model, you are not going to be able to use a standard handset cable, but the cable does use straight-through communication, and the connector type is RJ9. It is a 4-wire, two-line cable. You can try experimenting with your own cabling, but most likely you will need our comm. cable with part number 0W6002B. This can typically be obtained only through calling into our technical support line @ 1-800-800-4272, or you can try checking through an APC distributor.
in addition to the cable that Erasmus mentioned, double check the little microlatch on the back of the communication card on the XR frame. this is the card that has the RJ9 connections of where you are plugging the cable into.
brobins3d_apc
Just an FYI: that part number is no longer "regularly" sellable from APC. They are terming it as a parts and material item and the shipping is a flat rate of $200. No, that's not a misprint, two hundred dollars.
So, you say it's straight wired, pin 1 to pin 1, etc?
yes, technically its not a sellable SKU and you'd have to go through the time and materials program.
if you confirm your email address is correct in your profile (you dont need type in a post), i can contact you about a cable to try.
the microlatch is basically on the card itself. it is the thumbscrew on the right hand side of the status LED that isnt lit. it is attached to a little square piece of metal which is the microlatch. make sure that screw is tight and if it is, try leaning on that square piece to see if the LED comes on so then we know thats the issue.
let me know if that helps and about the cable.
brobins3d_apc
Ok, found the microlatch. No green light. Reseated card just in case and no change.
My email is correct.
Bill
brobins3d_apc
That's interesting. I had an XR frame go bad at another site and assumed it was some electrical problem with the frame, but in fact it could have been the SYXRCC? Have to file that away for next time.
i am sending you the cable but honestly, majority of the time it is the SYXRCC.
what do you see on the display on the front of the frame??
brobins3d_apc
This was originally posted on APC forums on 10/23/2008
Nothing shows on the front of the frame.
This reply was originally posted by Angela on APC forums on 10/23/2008
and you have the DC power cable plugged into the UPS portion, right? it is sounding more and more like SYXRCC 😕
brobins3d_apc
Yes, the DC cable is plugged in.
So, it sounds like you are saying that even without the communication cable plugged in, the display should be active? Is that correct? Remember that I've got a handset cord plugged in currently, which was designated as not workable for this model of Symmetra.
i'd have to test it to be 100% sure. i want you to try that cable i shipped to you first to be sure thats not the case. ill try and check it out tomorrow when i have access to one to check out.
regardless if its not, you will have the cable for when we fix it.
brobins3d_apc
This was originally posted on APC forums on 11/5/2008
The communication cable fixed the issue. So, to reiterate, for my model of XR frame, a handset cord will not work.
Thanks for the assistance.
Bill
brobins3d_apc
Interesting information. Wish I'd known that for an earlier cabinet that went bad, I wouldn't have thrown the cabinet away.