84622members
353937posts
Symmetra PX 40
Beekeeper_apc
171
Symmetra PX 40
This was originally posted on APC forums on 5/30/2015
Is the Static Switch module, P/N SYSW40KF hot swappable with the load remaining on the UPS as is normal?
I know the identity board has to be changed to the replacement Static Switch, but can you replace the Static Switch module like you would a redundant Power Module?
JS
Tags (4)
Beekeeper_apc
Re: Symmetra PX 40
This was originally posted on APC forums on 6/1/2015
Angela,
Thank you for the fast and informative reply.
2 Replies 2
Re: Symmetra PX 40
This reply was originally posted by Angela on APC forums on 6/1/2015
I'd definitely recommend verifying this with your local 3 phase support team via email or phone if this is not being done by APC or an authorized service provider, but what I found was:
Static Switch Modules on the Symmetra PX 80 and 100 may be hot swapped. This procedure is not possible on the Symmetra PX 40 and ISX 20K All-in-one.  In some cases, the static bypass feature may still be available even though the SSW is reporting as failed. If the alarm is one of the three listed below then static bypass is available through the Power view (on MIM v17.0 >).
1. Overload in PSU (Severity Level 2)
2. Fan_Fault (Severity Level 2)
3. Heatsink over temp (Severity Level 2)
If the SSW fault is on a PX40 and not one of the three alarms listed above then a shutdown will be required to change the SSW.
Beekeeper_apc
Re: Symmetra PX 40
Angela,