Symmetra LX shows only 117 vin but works ok

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
rmurcia_apc
Cadet
0 Likes
1
117

Symmetra LX shows only 117 vin but works ok

This was originally posted on APC forums on 11/20/2015


I have 3 symmetra LX units. One of them diplays 117 vin. When I go to the Vin Vout page I have the correct measures. 1 Vin 117 2 vin 116  3 vin 222

Same error with both IM-

Does  anyone  knows how to correct this?

Tags (3)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
117

Re: Symmetra LX shows only 117 vin but works ok

This reply was originally posted by David on APC forums on 11/24/2015


Hi Roberto,

I am thinking you are talking about the main screen of the display showing the 117 volts in. The older models of the display showed the voltage input/output on phase 1, where the recent displays will show the voltages across both phases. This only applies to the "main view" or screen saver, so to speak. As you noted, you can get all of the voltages by going into the status menu. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
118

Re: Symmetra LX shows only 117 vin but works ok

This reply was originally posted by David on APC forums on 11/24/2015


Hi Roberto,

I am thinking you are talking about the main screen of the display showing the 117 volts in. The older models of the display showed the voltage input/output on phase 1, where the recent displays will show the voltages across both phases. This only applies to the "main view" or screen saver, so to speak. As you noted, you can get all of the voltages by going into the status menu.