I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.
Online Manuals lack detailed information.
Is there a way to extract a dry contact from this bypass: SBP16KRMI4U
Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models
Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).
Posted: 2021-06-29 12:16 AM
This reply was originally posted by Federico on APC forums on 4/19/2010
I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.
Online Manuals lack detailed information.
Is there a way to extract a dry contact from this bypass: SBP16KRMI4U
Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models
Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).
Posted: 2021-06-29 12:16 AM
This reply was originally posted by Federico on APC forums on 4/22/2010
Thanks, I checked this by myself yesterday after dismantling the unit. 😃
Posted: 2021-06-29 12:16 AM
This reply was originally posted by Federico on APC forums on 4/19/2010
I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.
Online Manuals lack detailed information.
Is there a way to extract a dry contact from this bypass: SBP16KRMI4U
Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models
Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.