Symmetra LX Bypass Dry Contact Output

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
2
144

Symmetra LX Bypass Dry Contact Output

This question was originally posted by Federico on APC forums on 4/19/2010


I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.

Online Manuals lack detailed information.

Is there a way to extract a dry contact from this bypass: SBP16KRMI4U

Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models

Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
144

Symmetra LX Bypass Dry Contact Output

This reply was originally posted by Federico on APC forums on 4/19/2010


I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.

Online Manuals lack detailed information.

Is there a way to extract a dry contact from this bypass: SBP16KRMI4U

Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models

Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
144

Re: Symmetra LX Bypass Dry Contact Output

This reply was originally posted by Federico on APC forums on 4/22/2010


Thanks, I checked this by myself yesterday after dismantling the unit. 😃

BillP
Administrator Administrator
Administrator
0 Likes
0
145

Symmetra LX Bypass Dry Contact Output

This reply was originally posted by Federico on APC forums on 4/19/2010


I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.

Online Manuals lack detailed information.

Is there a way to extract a dry contact from this bypass: SBP16KRMI4U

Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models

Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).