Symmetra 4kva (8000) - RIM died again?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra 4kva (8000) - RIM died again?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

0 Likes
4
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

Symmetra 4kva (8000) - RIM died again?

We have a Symmetra 4kva (short frame) that has run great for years.  Yesterday we took it down for a good cleaning.  On bringing it back up we experienced a RIM failure (seems strange that it worked fine until the power off).  We replaced the RIM a few years ago after a similar experience.  I'm suspicious...before we spend another $800 on parts I want to make sure there's nothing we're missing.

On first power up after cleaning the LCD displayed showed input power out of range (which I know it was not).  Is that a clue? 

The RIM shows no LED's on power on.  We removed the RIM and the MIM shows only the rightmost light green LED on (left to right MIM LEDS: red/lightgreen/darkgreen/lightgreen).

The status dump of the RIM shows:

000 01 0 00 ****

1D FF FF FF FF 1

20******* *****

which I'm guessing is just default values....

Can anyone shed some light?  Is this really just another coincidental RIM failure?  (We did not remove the RIM or MIM during cleaning)

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • failure
  • mim
  • rim
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:21 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:21 AM

OK, after some investigation, here are some recommendations. Please note that I'll assume you prepare your load accordingly or put the UPS in bypass as to avoid any issues. (Let me know if any questions on that before proceeding.)

To begin with, what we'd do is pull the RIM out and inspect it for any bent pins. Once you remove it and are looking for any bent pins which can cause this, verify that the fault does clear with the RIM removed. Assuming it does, another idea is to perhaps remove all modules besides the MIM (including any power modules) and then make sure there are no faults. You can also toggle the System Enable switch at this time too (which is OK to do with a load if you're in maintenance bypass) and then once it turn's back on, try the RIM again and see if the fault comes right back. To me, this at least helps rule out any other strange issues with any other modules.

If nothing points to a problem with bent pins or other problems, then it is likely this is just a coincidence that the RIM has failed again. Did it look relatively clean or do you have a dusty environment where perhaps this module has gotten clogged with dust which is becoming conductive and shorting something (as an example)?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

hello,

Is this the short little beige Symmetra Power Array/"Miniframe" or is this a Symmetra LX (which is black/gray in color)?

I wanted to double check too - did you ** some values out or is that literally what you're seeing on the powerview LCD screen? Can you confirm where you got the status dump from because no matter if it is a Symmetra Power Array, the dump data format doesn't look right to me and I can't interpret it.

Do you have the pre-installed UPS Network Management Card configured where we can also review the logs from? (And if you did not *** some values out in the raw status, what does the raw status show in the Network Management Card?)

Here are instructions on downloading the log files if you can get them -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Reply

Link copied. Please paste this link to share this article on your social media post.

ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

It's the beige Power Array symmetra.  I read the raw data from the LCD console attached to the UPS.  The data above is exactly what it showed onscreen (lots of stars as noted above)

Does that mean something?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:48 AM . Last Modified: ‎2024-03-12 03:21 AM

Actually, I have one of these UPS units and ours is up and running online as it should be. The RIM status dump does have some **** in it. Apparently I have forgotten this over the years..

Let me request some more expertise on this one smile and see what we can find out for us now that *** is confirmed as normal.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:21 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:21 AM

OK, after some investigation, here are some recommendations. Please note that I'll assume you prepare your load accordingly or put the UPS in bypass as to avoid any issues. (Let me know if any questions on that before proceeding.)

To begin with, what we'd do is pull the RIM out and inspect it for any bent pins. Once you remove it and are looking for any bent pins which can cause this, verify that the fault does clear with the RIM removed. Assuming it does, another idea is to perhaps remove all modules besides the MIM (including any power modules) and then make sure there are no faults. You can also toggle the System Enable switch at this time too (which is OK to do with a load if you're in maintenance bypass) and then once it turn's back on, try the RIM again and see if the fault comes right back. To me, this at least helps rule out any other strange issues with any other modules.

If nothing points to a problem with bent pins or other problems, then it is likely this is just a coincidence that the RIM has failed again. Did it look relatively clean or do you have a dusty environment where perhaps this module has gotten clogged with dust which is becoming conductive and shorting something (as an example)?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of