Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the Schneider Electric Community! We have moved to a new address: community.se.com — bookmark it today and contact SchneiderCommunity.Support@se.com if you have any questions!
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82748members
350524posts

Static Swich Module on PX 40kVA is hot swappable?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
3
140

Static Swich Module on PX 40kVA is hot swappable?

This question was originally posted by Franklin on APC forums on 11/26/2012


Is the Static Switch Module (SSW) on a PX 40kVA hot swapp??

Symmetra PX 40kW Scalable to 40kW N+1, 208V
PX 40kVA model: SYCF40KF or SY40K40F
SSW model: SYSW40KF

the Static Swich module can be pull out without drop the load?
is hot swappable?

Attachments

Accepted Solutions
Battman_apc
Commander
Commander
0 Likes
0
140

Re: Static Swich Module on PX 40kVA is hot swappable?

This was originally posted on APC forums on 6/13/2013


In terms of the loads (servers ) staying up and NOT having to be shut down, it is swappable. I'd recommend getting an APC Field Service Engineer in to do this as it is not obvious how to do it to the end user, nor well documented. Good luck !

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
140

Re: Static Swich Module on PX 40kVA is hot swappable?

This reply was originally posted by Angela on APC forums on 11/27/2012


it is NOT hot swappable - you need to shutdown the UPS and in full maintenance bypass.

narf2013_apc
Ensign
Ensign
0 Likes
0
140

Re: Static Swich Module on PX 40kVA is hot swappable?

This was originally posted on APC forums on 6/13/2013


you are right it´s not hotswappable....frown

Battman_apc
Commander
Commander
0 Likes
0
141

Re: Static Swich Module on PX 40kVA is hot swappable?

This was originally posted on APC forums on 6/13/2013


In terms of the loads (servers ) staying up and NOT having to be shut down, it is swappable. I'd recommend getting an APC Field Service Engineer in to do this as it is not obvious how to do it to the end user, nor well documented. Good luck !