SmartUPS 3000 SU3000RM Won't "Cold Start" from battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 3000 SU3000RM Won't "Cold Start" from battery
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

0 Likes
6
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

SmartUPS 3000 SU3000RM Won't "Cold Start" from battery

A year ago I got a SU3000RM and didn't have any batteries to test it with. So I had hooked it up to 2 small wall wart SMPS that were in series with eachother. (30V + 18V for 48v total)  just to test to see if the unit would power up before purchasing batteries.  It cold started  doing this the first couple of times but it seems to have fried something. Possible a voltage spike from one of the SMPS wall warts. I didn't put any load on the unit at the time of testing with the wall warts because they were only rated for an amp or two.

Now the unit functions normally if you plug it in first, power it up and the power fails. (I now have batteries to test it properly)  but won't do a cold start.

Attempting to do a cold start causes the overload light to turn on an and the alarm beeps.

Any Idea where to start looking for problems? Bad MOVs?(are there any in the output circuit?) Bad diodes? Faulty FET? 

It seems to be drawing more current on start up than it should but my DMM isn't quick enough to give a reliable reading.

It is a SU3000RM J3U with a 640-0734K PCB in it.

Thanks for any advice

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

On 13/4/2021 10:52 AM, Mikey said:

Hopefully that was the issue.

Sounds like a good result. Nice work, and thanks for coming back to report. Many don't.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

I'd start by querying the status registers to narrow down what the UPS thinks the fault is. Towards the bottom of this page gives you the bit definitions, and looking at the protocol will tell you how to get that data from the UPS : https://networkupstools.org/protocols/apcsmart.html

Start with registers 1, 2 & 3.

It'd also be interesting to check both the input and output voltage measurements and the power measurement to make sure they are about where they should be (Check voltages while plugged in and on mains, and the load with a known load of some kind).

None of the units I've seen have MOVs on the UPS side of the input isolation relay and that should be open for a cold start.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

Thank you for  your reply.  Sorry for the delay in writing back. Things have suddenly become really busy at work and I haven't had much free time to play around with projects. I will definitely get a serial cable built and test this out as soon as I can.  Hopefully in the next couple of weeks. I will get back to you with the results. Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:14 PM

Things ended up being more busy than I expected. I have finally gotten back to working on this UPS. Got a serial connection working with it and can see when it says there is a power failure but can't see any error in the terminal when it shows overload on start up.

Tested and works in normal power failure mode with no obvious problems.
Cold booting / starting it from battery fails every time with overload error, but with a light bulb connected to the output it flashes on for a split second. 

Tried disconnecting output from transformers before it goes through the Current Transformers on the output of the PCB. Still same overload error.

Start-up curren't from batteries doesn't seem excessive, won't blow the 4A fuse I had on hand and threw in to see.

I'm not sure how to get diagnostic info from the serial terminal on this to see what else could be the problem.

Next thing I want to try is to bypass the Current transformers (CT1 CT2) on the hot and neutral output and see if that makes a difference. Maybe just remove them and try?

Thanks in advance for any help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

I have gotten it to cold start now. I'm not sure it is fixed yet but it seems to be. I replaced C48 a 6.3v 100uf electrolytic capacitor after studying the schematic for along time to see what might be the problem. It is in the circuit that the current transformer is part of. Just as a guess I thought it might be causing problems, especially since it is a CapXon cap. Hopefully that was the issue.

I imagine there are other bad capacitors on this board because they are mostly CapXon. So I plan to replace most of the electrolytics on it with some Nichicon caps so this unit will hopefully operate for years to come.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

The double conversion architecture provides tight voltage regulation, frequency regulation ,and zero transfer time to battery during power events.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

On 13/4/2021 10:52 AM, Mikey said:

Hopefully that was the issue.

Sounds like a good result. Nice work, and thanks for coming back to report. Many don't.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of