SmartConnect capability?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BenBBTS_apc
Cadet
0 Likes
1
251

SmartConnect capability?

This was originally posted on APC forums on 8/5/2020


Does SmartConnect have the ability to shutdown a VMware host? If so, where can I find information on requirements to get this set up? We are looking to get graceful shutdown capabilities set up at several of our customers and are trying to figure out what equipment to get. Many of them only have one host and only a couple VMs and no vCenter server. Getting a UPS with an NMC would be overkill for these customers, so we were hoping to be able to get the same functionality with a UPS with SmartConnect. Of course, if that's not possible, then that's that.

Thank you for any feedback!


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
251

Re: SmartConnect capability?

This reply was originally posted by Gavan on APC forums on 8/6/2020


Hi Ben,

Sorry but the Smart Connect port is only for connecting to the APC cloud monitoring service, however depending on the version of VMWare you are running it is possible to shutdown the UPS with Powerchute Business Edition, (due to changes by VMWare this option is not compatible with some later versions).

It is also possible to connect the UPS to a machine running PCBE and then have PCBE execute a script to shutdown the hosts when the battery is low, this is not supported as such and an NMC would work better but it is up to you.

-Gavan 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
252

Re: SmartConnect capability?

This reply was originally posted by Gavan on APC forums on 8/6/2020


Hi Ben,

Sorry but the Smart Connect port is only for connecting to the APC cloud monitoring service, however depending on the version of VMWare you are running it is possible to shutdown the UPS with Powerchute Business Edition, (due to changes by VMWare this option is not compatible with some later versions).

It is also possible to connect the UPS to a machine running PCBE and then have PCBE execute a script to shutdown the hosts when the battery is low, this is not supported as such and an NMC would work better but it is up to you.

-Gavan