Smart-UPS x 2000 critical - Voltage exceeds... A battery charger fault exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Gracew_apc
Crewman
Crewman
0 Likes
2
493

Smart-UPS x 2000 critical - Voltage exceeds... A battery charger fault exists

This was originally posted on APC forums on 12/30/2015


Good Day and thank you for your time,

I have a UPS that I monitor in a remote location.  

I can dispatch a tech to perform maintenance but I cannot perform much troubleshooting without them.

With that said I have a Smart-UPS X 2000 and an External Battery Pack which was installed this year.

It has two Critical Alarms and I see the battery is not charging fully.

UPS Network Management Card 2

  • The battery voltage exceeds the nominal battery voltage rating.
  • A battery charger fault exists.

UPS Network Management Card 2

Model: Smart-UPS X 2000
SKU: SMX2000LVNC
Firmware Revision: UPS 07.4 (ID1003)
Manufacture Date: 09/27/2014
Apparent Power Rating: 1920 VA
Real Power Rating: 1800 W
Internal Battery SKU: APCRBC143
External Battery SKU: APCRBC143

Basically I see my options as such:

Get the chassis replacement under warranty and have the tech do a swap

Get replacement batteries and have a tech do that swap

If necessary I can walk an unqualified individual through performing the brain dead procedure prior to the above options.

Attachments
Tags (1)

Accepted Solutions
Gracew_apc
Crewman
Crewman
0 Likes
0
493

Re: Smart-UPS x 2000 critical - Voltage exceeds... A battery charger fault exists

This was originally posted on APC forums on 12/30/2015


Thanks!

I appreciate the quick response and confirmation.

See Answer In Context

2 Replies 2
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
493

Re: Smart-UPS x 2000 critical - Voltage exceeds... A battery charger fault exists

This was originally posted on APC forums on 12/30/2015


Hi Wayne,

The brain dead is the troubleshooting step I would perform. With the unit being only a little over a year old I would not expect the issue to be bad batteries. If the fault returns after the brain dead the unit would likely need to be replaced. 

I would call your local support when you have someone in front of the unit so they can get all the information they need and then perform that brain dead procedure. The procedure is rather simple and as long as the individual on site is comfortable, the tech support rep will be able to walk them through it. 

Gracew_apc
Crewman
Crewman
0 Likes
0
494

Re: Smart-UPS x 2000 critical - Voltage exceeds... A battery charger fault exists

This was originally posted on APC forums on 12/30/2015


Thanks!

I appreciate the quick response and confirmation.