Smart-UPS X 3000 - UPS: In bypass in response to an internal hardware fault.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 3000 - UPS: In bypass in response to an internal hardware fault.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:31 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
1
3402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:31 AM . Last Modified: ‎2024-03-18 04:35 AM

Smart-UPS X 3000 - UPS: In bypass in response to an internal hardware fault.

I have a UPS that has sent out an alert. Do you know what would cause this? I need to do something quickly.

Thanks in advance for your help!

 

Attachments
data.zip
event.zip
config.zip
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:31 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:31 AM . Last Modified: ‎2024-03-18 04:35 AM

Hi Roy,

I took a quick look. I see your UPS was manufactured in 2011. I also noted in the event log that you're having hot battery issues..

03/08/2016      23:24:31  UPS: The internal battery temperature exceeds the critical threshold. 0x012C

I also see a lot of these since your AC input voltage to the UPS is a little low...

03/10/2016 09:12:16 UPS: No longer compensating for a low input voltage. 0x010C
03/10/2016 09:12:16 UPS: Compensating for a low input voltage. 0x010B

I recommend you maybe take a look at the physical UPS and battery and maybe put the back of your hand on it to check it out. But, I'd guess that you're very close to needing a new/replacement battery for the UPS. The event log is spammed with NTP update problems so I can't see that far back beyond a few days ago to see when the last UPS self-test was. It could probably detect the bad battery during its next self test which happens every two weeks. Long story short, I think the UPS went to bypass because you have a hot battery problem and need a new repalcement battery.

Secondly, the low AC input voltage you could investigate with the utility power feed to the UPS. Not sure if it is a data center power problem or utility provider power problem but it is not a UPS problem. The UPS is "boosting" the voltage to compensate for the low voltage. This issue is not tied to the battery issue nor why the UPS is in bypass due to a hardware fault.

Hope that helps.

P.S. - unrelated but your Network Management Card firmware is REALLY outdated. I recommend we get that upgraded after you address the other more critical issues going on. The new firmware would tell you the replacement battery part number right in the interface and logging would be better and more detailed. Lots of security fixes too.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:31 AM . Last Modified: ‎2024-03-18 04:35 AM

0 Likes
0
3402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:31 AM . Last Modified: ‎2024-03-18 04:35 AM

Hi Roy,

I took a quick look. I see your UPS was manufactured in 2011. I also noted in the event log that you're having hot battery issues..

03/08/2016      23:24:31  UPS: The internal battery temperature exceeds the critical threshold. 0x012C

I also see a lot of these since your AC input voltage to the UPS is a little low...

03/10/2016 09:12:16 UPS: No longer compensating for a low input voltage. 0x010C
03/10/2016 09:12:16 UPS: Compensating for a low input voltage. 0x010B

I recommend you maybe take a look at the physical UPS and battery and maybe put the back of your hand on it to check it out. But, I'd guess that you're very close to needing a new/replacement battery for the UPS. The event log is spammed with NTP update problems so I can't see that far back beyond a few days ago to see when the last UPS self-test was. It could probably detect the bad battery during its next self test which happens every two weeks. Long story short, I think the UPS went to bypass because you have a hot battery problem and need a new repalcement battery.

Secondly, the low AC input voltage you could investigate with the utility power feed to the UPS. Not sure if it is a data center power problem or utility provider power problem but it is not a UPS problem. The UPS is "boosting" the voltage to compensate for the low voltage. This issue is not tied to the battery issue nor why the UPS is in bypass due to a hardware fault.

Hope that helps.

P.S. - unrelated but your Network Management Card firmware is REALLY outdated. I recommend we get that upgraded after you address the other more critical issues going on. The new firmware would tell you the replacement battery part number right in the interface and logging would be better and more detailed. Lots of security fixes too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of