Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82523members
350129posts

Smart-UPS VT 30KVA - Power Module Total Failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
cg6999_apc
Crewman
Crewman
0 Likes
6
283

Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 6/8/2009


Hi All,

My company has a Smart-UPS VT 30KVA with XR battery enclosure, which is nearly fully populated with packs. The unit is just over three years old, and has never been loaded to more than 60%

The unit has been in operation without fault in a datacentre environment (with controlled temperature and humidity) for it's entire life. Every 2 weeks it runs a self-test, which has always passed.

A few days ago it seems the power module completely failed. It went into soft bypass, the display went blank, and the remote management card stopped responding. No extraneous power conditions or environmental factors were recorded by our monitoring equipment at the time of the failure.

Fortunately it did not drop the load, and we have now bypassed the UPS completely.

Now the UPS will not power up at all - when given power (via the maintenance panel) is does not respond at all (no lights, no noise, no sign of life of any kind).

This has generally been (remotely) diagnosed by APC tech support as a failure of the power module which, it seems, is almost as expensive to replace as the cost of the entire UPS system.

Does anybody have any experience of this failure? Are there any other options - for instance, can the power module be diagnosed and repaired rather than being totally replaced?

Any advice you can offer would be gratefully received. It seems to me that a system like this, when used in basically ideal conditions, should not suffer a total failure after just 3 years.


Accepted Solutions
suleman_khosa_apc
Crewman
Crewman
0 Likes
0
283

Re: Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 2/24/2012


hi all

I checked website and get too much knowledge from forums.

I am new in APC and today i collected one PAC UPS 30 KVA smart UPS from one client

When i checked its bank voltages are OK but UPS is totall death and no indication.

In this power module number is SUVTPM30KH

i need its manuals for start up and maintenance manual and software.
if any body have then please let me inform by email
subhani_engr1@yahoo.com

See Answer In Context

6 Replies 6
cg6999_apc
Crewman
Crewman
0 Likes
0
284

Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 6/8/2009


Hi All,

My company has a Smart-UPS VT 30KVA with XR battery enclosure, which is nearly fully populated with packs. The unit is just over three years old, and has never been loaded to more than 60%

The unit has been in operation without fault in a datacentre environment (with controlled temperature and humidity) for it's entire life. Every 2 weeks it runs a self-test, which has always passed.

A few days ago it seems the power module completely failed. It went into soft bypass, the display went blank, and the remote management card stopped responding. No extraneous power conditions or environmental factors were recorded by our monitoring equipment at the time of the failure.

Fortunately it did not drop the load, and we have now bypassed the UPS completely.

Now the UPS will not power up at all - when given power (via the maintenance panel) is does not respond at all (no lights, no noise, no sign of life of any kind).

This has generally been (remotely) diagnosed by APC tech support as a failure of the power module which, it seems, is almost as expensive to replace as the cost of the entire UPS system.

Does anybody have any experience of this failure? Are there any other options - for instance, can the power module be diagnosed and repaired rather than being totally replaced?

Any advice you can offer would be gratefully received. It seems to me that a system like this, when used in basically ideal conditions, should not suffer a total failure after just 3 years.

Erasmus_apc
Sisko
Sisko
0 Likes
0
284

Re: Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 6/9/2009


Here we are:

The APC tech that you previously spoke with was accurate in deducing that the power module is the most probable point of failure and needs to be replaced. The PM could be failed for any number of reasons (PSU fault, etc.) - but any failed component in the PM requires the entire PM be replaced (the VT has very few modular parts). The symptom of the UPS being dark, but not dropping the load, is an indication that the static switch still functions, and is not indicative of a catastrophic UPS failure. However, the PM is the most major component of the UPS as it contains logic, inverters, etc.

The easiest test is to reseat the PM with the UPS is completely bypassed. After reseating, does the UPS startup? If not, a site visit may be in order, or simply replace the PM. Unfortunately, without access to controller logs, NMC logs, etc we can't tell what has caused the PM to fail.

Edit: I would just call into our three-phase tech support team @ 1-800-800-4272 and determine a resolution.

Message was edited by: Erasmus

Erasmus_apc
Sisko
Sisko
0 Likes
0
284

Re: Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 6/9/2009


Looking into your inquiry with our 3-phase team. Will respond shortly.

cg6999_apc
Crewman
Crewman
0 Likes
0
284

Re: Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 6/9/2009


Thanks for responding. I did actually try re-seating the power module - I've also done a basic visual inspection of it to look for loose wires, blown components, and the like - but no joy.

One additional question springs to mind - the power module in our UPS is part number OG-SUVTPM30KH. This UPS is a UK one, set to 400v. Does anyone know if the power modules are identical in different regional variants? For example, it seems the US region version of the power module has the same part number. Do the internal electronics adjust to different input voltages, or do I need to specifically get a UK power module?

Thanks

Erasmus_apc
Sisko
Sisko
0 Likes
0
284

Re: Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 6/9/2009


You would need to contact Europe/EMEA support for the correct power module. The North American model PM is 208v.

suleman_khosa_apc
Crewman
Crewman
0 Likes
0
284

Re: Smart-UPS VT 30KVA - Power Module Total Failure

This was originally posted on APC forums on 2/24/2012


hi all

I checked website and get too much knowledge from forums.

I am new in APC and today i collected one PAC UPS 30 KVA smart UPS from one client

When i checked its bank voltages are OK but UPS is totall death and no indication.

In this power module number is SUVTPM30KH

i need its manuals for start up and maintenance manual and software.
if any body have then please let me inform by email
subhani_engr1@yahoo.com