Smart-UPS SU420INet and Server 2008 R2

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
angares_apc
Ensign
Ensign
0 Likes
11
828

Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/2/2011


Hello everybody,

is it possible to use a Smart-UPS SU420INet with Windows Server 2008 R2 x64? Has anybody tested it and can i use official apc software?

Thanks for answers!

Nils


Accepted Solutions
angares_apc
Ensign
Ensign
0 Likes
0
828

Re: Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/2/2011


Thank you, I'll post my experience!

See Answer In Context

11 Replies 11
BillP
Administrator Administrator
Administrator
0 Likes
0
828

Re: Smart-UPS SU420INet and Server 2008 R2

This reply was originally posted by Angela on APC forums on 8/2/2011


as far as i know, this UPS still should work with powerchute business edition with the 940-0024 or 940-1524 APC serial cable.

here is the compatibility chart for PCBE -> http://www.apcmedia.com/salestools/ASTE-6Z5QEV_R27_EN.pdf

BillP
Administrator Administrator
Administrator
0 Likes
0
828

Re: Smart-UPS SU420INet and Server 2008 R2

This reply was originally posted by Angela on APC forums on 8/2/2011


since that UPS is older, it was most likely not actually tested but should work just fine since that UPS is simple signaling.

angares_apc
Ensign
Ensign
0 Likes
0
829

Re: Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/9/2011


Okey, there is no problem installing the UPS on Windows Server 2008 R2 x64 with PowerChute, but the Shutdown doesn't work 😞 I think, it's a Configuration Problem, any ideas?

BillP
Administrator Administrator
Administrator
0 Likes
0
829

Re: Smart-UPS SU420INet and Server 2008 R2

This reply was originally posted by Angela on APC forums on 8/9/2011


what is happening? can you show us your configuration via screenshot or similar? generally if you plug everything in and install the software, then by default, the graceful shutdown should begin when the UPS has a low battery (when 2 minutes of runtime is left).

did you connect the serial cable between the server and UPS? if so, whats the part number? it should be engraved on the connector.

angares_apc
Ensign
Ensign
0 Likes
0
827

Re: Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/9/2011


I unplugged the power connector. The PC was runnig with battery power but didn't shutdown. I was not logged in as Administrator. When I logged in, the Shutdown starts immediately. After Restart I logged in once again and then the PC switched off immediately.
I thought, that the PC would shutdown after 3 minutes. Need PowerChute Administration-Rights or something like that? Are the Screenshots okey?

Sorry for my english...

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
827

Re: Smart-UPS SU420INet and Server 2008 R2

This reply was originally posted by Angela on APC forums on 8/9/2011


hi - no problem.

i asked around and apparently not being logged in was the problem. when you log out of windows server, it stops all processes and this is what happened.

take a look at this link -> http://nam-en.apc.com/app/answers/detail/a_id/9045

angares_apc
Ensign
Ensign
0 Likes
0
827

Re: Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/9/2011


Thank you! I will test it 🙂

And my Configuration is okey?

Message was edited by: angares

angares_apc
Ensign
Ensign
0 Likes
0
826

Re: Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/9/2011


Hm, I read the Knowledge entry, but are you shure, it's the right solution for my problem? They talk about the logon screen and when I logged of from the server, the "CTRL+ALT+DEL-Screen" appears. Shall I use "auto-login" for administrator?

Message was edited by: angares

BillP
Administrator Administrator
Administrator
0 Likes
0
827

Re: Smart-UPS SU420INet and Server 2008 R2

This reply was originally posted by Angela on APC forums on 8/9/2011


yeah, i think you need to change it or leave it locked, but logged in and lock the screen?

also, on your configuration, are you running a command file? how long does your server take to shutdown?

angares_apc
Ensign
Ensign
0 Likes
0
827

Re: Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/10/2011


Now i tested it and "autologin" was the solution. The server switched off after 4 minutes, as configured.

Thank you so much for your help!

angares_apc
Ensign
Ensign
0 Likes
0
829

Re: Smart-UPS SU420INet and Server 2008 R2

This was originally posted on APC forums on 8/2/2011


Thank you, I'll post my experience!