Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Smart UPS RT 3000 beeping and switching between online and battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS RT 3000 beeping and switching between online and battery
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:33 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
7
1803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:33 AM . Last Modified: ‎2024-03-12 03:39 AM

Smart UPS RT 3000 beeping and switching between online and battery

See the video below. Our UPS is doing this on a daily basis for about an hour then it's fine for the rest of the day.. Any ideas would be greatly appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

I would start by braindeading the UPS and then connecting things one by one back to the UPS, including the NMC.


To braindead, you'll need to turn off the UPS and again, just double check for any communication cables. (The only time I've honestly seen this is when a faulty serial cable was connected.) Once the UPS is off, remove AC power (or flip the input breaker). Then, hold down the UPS off button and ensure the LEDs flash and/or you hear an audible click. Re-apply AC power or restore the breaker and close it and then power the UPS again and observe.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:33 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:33 AM . Last Modified: ‎2024-03-12 03:39 AM

Hi, what time of the day is this happening ?  Its not uncommon for there to be noisy power in buildings for brief periods of time on a cyclical basis - Eg, many buildings have BMS systems which turn down fans and heating hardware overnight then promptly turn them on again at 7:00 or 8:00 AM prior to human occupancy. These types of inductive loads when kicking in can cause brief voltage sags that will cause your ups to react this way. Same thing can happen if there are elevators in a building and in the morning they are heavily used while everyone arrives then afterwards there is sporadic usage....

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:33 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:33 AM . Last Modified: ‎2024-03-12 03:39 AM

Can you let me know how you have this set up - what's connected to it for load, communication cables, etc? Also, can you visually verify if you have a serial cable attached to the rear of this UPS? A picture will also help (since you were able to do a video which was nice). This could be due to a faulty serial cable potentially that has just began to start failing. We've identified an older batch of serial cables we saw this with once before that caused this type of symptom and it typically happens over time and maybe is just starting to develop.

Secondly, if this UPS has a UPS Network Management Card installed, the logs from it would be extremely useful to see what the UPS is logging. PowerChute Business edition would also provide logs - let me know what you have and I can tell you how to get the logs if you're unsure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

Hi and thanks for your reply. Sorry for the delay getting back to you, I've only just managed to install the network management card in order to get to the logs.

There's no indication that there is anything wrong with the battery.. but it seems to be doing a lot of self tests.

event log attached.

Many Thanks

Dan

Attachments
event.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

Hi and thanks for the reply. Sorry for the delay getting back to you, I've only just managed to install the network management card in order to get to the logs.

I was in the building yesterday afternoon and no one else was in the building and it started doing this. Seems to be doing lots of self tests...

Thanks

Dan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

Yes - are any of those front panel buttons stuck? Or I don't know if you can fiddle with them to see if they are stuck and if the self tests stop. Also, could you visually verify whether or not a serial cable is attached to the rear of the UPS in the DB-9 port? (And we'd eventually want to remove it once we know what the other end is connected to.)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

Hi

i'll check for struck buttons but don't think so. No serial cable is connected.

thanks

dan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

0 Likes
0
1802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:39 AM

I would start by braindeading the UPS and then connecting things one by one back to the UPS, including the NMC.


To braindead, you'll need to turn off the UPS and again, just double check for any communication cables. (The only time I've honestly seen this is when a faulty serial cable was connected.) Once the UPS is off, remove AC power (or flip the input breaker). Then, hold down the UPS off button and ensure the LEDs flash and/or you hear an audible click. Re-apply AC power or restore the breaker and close it and then power the UPS again and observe.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of