Smart-UPS RT 3000 XL with input power problems

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 3000 XL with input power problems
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
7
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

Smart-UPS RT 3000 XL with input power problems

I started getting e-mails from the battery in question stating "Warning - UPS: On battery power in response to rapid change of input.". This would immediately be followed up another message saying "Informational - UPS: No longer on battery power.".

After logging in and looking at the battery i see that the last battery transfer is saying "Unacceptable utility voltage rate of change". Also the Input Voltage is 206VAC and the Output Voltage is 209VAC. I'm not quite sure what this means, i'm guessing it means it's outputting more than it's brining in? I'm not entirely sure why - there have been no changes to the power circuit.

Any information you folks could provide would be much apprecaited.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

Hi,

Seems like there is really a rapid fluctuation coming from the input source and as what buzz said, the rate of change is the reason for the UPS to go on battery. The reason for having a 209V is because of the floating voltage. Since the the topology of this UPS is an Double Online Conversion, meaning all input voltage is passing through the battery (AC-DC) then to the output(DC-AC)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

I started getting e-mails from the battery in question stating "Warning - UPS: On battery power in response to rapid change of input.". This would immediately be followed up another message saying "Informational - UPS: No longer on battery power.".

After logging in and looking at the battery i see that the last battery transfer is saying "Unacceptable utility voltage rate of change". Also the Input Voltage is 206VAC and the Output Voltage is 209VAC. I'm not quite sure what this means, i'm guessing it means it's outputting more than it's brining in? I'm not entirely sure why - there have been no changes to the power circuit.

Any information you folks could provide would be much apprecaited.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

Hi,

If you can provide us the [data logs|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9321&p_created=1213880132&p...] from the network management card, that would be a big help. Also, add the the firmware that the card is using under, administration>general>about.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

Attached files as requested.

Also as requested firmware information:

Model Number: AP9619
Serial Number: BA0905008652
Hardware Revision: A10
Manufacture Date: 01/28/2009
MAC Address: 00 C0 B7 D6 B6 CE
Management Uptime: 164 Days 3 Hours 45 Minutes

Attachments
APC.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

Hi Jyost,

Looking at the data logs, seems like you have you a 10min interval. I would suggest you to change it like for a minute so we can map out the Input voltage change(Logs>Data>Interval). Also, can u provide me the screenshot of what you have under, UPS tab>Configuration>Power? I'd like to know what setting you have there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

Changed timer to 1 min - waited 10 mins and recaptured logs (attached). Also attached screenshot as requested.

Thanks in advance

Attachments
APC2.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

It sounds like normal operation to me... The topology of this UPS is to essentially recreate the power it's outputting, so it makes sense that the input and output aren't identical. Also, the "rate of change" reason for going to battery is caused by just that - the voltage fluctuated rapidly enough that the UPS determined it needed to go to battery to provide sufficient power to your equipment. Your data logs aren't likely to catch it since it sounds like a very brief instance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:18 AM . Last Modified: ‎2024-03-14 12:54 AM

Hi,

Seems like there is really a rapid fluctuation coming from the input source and as what buzz said, the rate of change is the reason for the UPS to go on battery. The reason for having a 209V is because of the floating voltage. Since the the topology of this UPS is an Double Online Conversion, meaning all input voltage is passing through the battery (AC-DC) then to the output(DC-AC)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now