Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82628members
350277posts

Smart UPS 3000 w/9630 will SNMP outlet control events be logged?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
bhmcintosh_apc
Cadet
0 Likes
1
104

Smart UPS 3000 w/9630 will SNMP outlet control events be logged?

This was originally posted on APC forums on 6/11/2014


We had a SmartUPS 3000 drop load.  The log indicated that the outlet groups were powered off and back on, but noone was logged onto the device, either cmd line or web.  If an SNMP write toggles the outlet groups off and on, would that be logged by the UPS?

06/11/2014
10:06:41
UPS: No longer compensating for a low input voltage.

06/11/2014
10:06:35
UPS: Compensating for a low input voltage.

06/11/2014
10:06:34
UPS: The output power is now turned on.

06/11/2014
10:06:34
UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on.

06/11/2014
10:06:34
UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.

06/11/2014
10:06:34
UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.

06/11/2014
10:06:34
UPS: No longer compensating for a low input voltage.

06/11/2014
10:06:33
UPS: The output power is turned off.

06/11/2014
10:06:33
UPS: No longer on battery power.

06/11/2014
10:06:32
UPS: On battery power in response to rapid change of input.

06/11/2014
10:06:32
UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay.

06/11/2014
10:06:32
UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.

06/11/2014
10:06:32
UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay.

06/11/2014
10:06:32
UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.

06/11/2014
10:06:32
UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.

06/11/2014
10:06:32
UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.

06/11/2014
10:06:32
UPS: Compensating for a low input voltage.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
104

Re: Smart UPS 3000 w/9630 will SNMP outlet control events be logged?

This reply was originally posted by Angela on APC forums on 6/11/2014


Hello,

Yes, these should be logged but I don't think it will necessarily say via SNMP but it does look like something told this to shutdown with a turn on delay after. You'd also want to make sure you don't have a random USB or serial cable attached to the UPS.

If you want to provide the full logs from the Network Management Card, I can take a further look to see if anything stands out. (Instructions here on how to do that if you need it -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
105

Re: Smart UPS 3000 w/9630 will SNMP outlet control events be logged?

This reply was originally posted by Angela on APC forums on 6/11/2014


Hello,

Yes, these should be logged but I don't think it will necessarily say via SNMP but it does look like something told this to shutdown with a turn on delay after. You'd also want to make sure you don't have a random USB or serial cable attached to the UPS.

If you want to provide the full logs from the Network Management Card, I can take a further look to see if anything stands out. (Instructions here on how to do that if you need it -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)