Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Smart-UPS 3000 discharge rate not matching runtime remaining

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Smart-UPS 3000 discharge rate not matching runtime remaining
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:27 AM

0 Likes
5
487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:27 AM

Smart-UPS 3000 discharge rate not matching runtime remaining

This question was originally posted by Mark on APC forums on 7/14/2014


Hi,

We have a Smart-UPS 3000 with typically a 15% load that started running on battery today.  It was on battery power for approximately 5 seconds, and in this time dropped to 90% capacity.

The UPS still shows a runtime remaining of 36 mins, but if it discharged at this rate then it would last less that a minute.

Is 5 seconds long enough to start calibrating the battery?  What was displaying the wrong value, the 90% capacity after 5 seconds, or the 36 min runtime?

Log:

07/14/2014    06:55:14    UPS: No longer on battery power.

07/14/2014    06:55:10    UPS: On battery power in response to distorted input.

07/14/2014    06:55:10    UPS: No longer compensating for a high input voltage.

07/14/2014    06:54:19    UPS: Compensating for a high input voltage.

07/14/2014    06:54:03    UPS: No longer on battery power.

07/14/2014    06:54:02    UPS: On battery power in response to distorted input.


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-29 08:28 AM

0 Likes
0
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:28 AM

This was originally posted on APC forums on 7/17/2014


I deal with a large number of UPS units in locations across the US.  Over the past few months I have been dealing with some VERY old UPS units and also some VERY old batteries.  Some of the UPS units were installed in the mid to late 90"s and a few more in the early 2000's.  By far, the majority of our units are from 2006-2007.  Some of the batteries in those units have never been replaced.  We have started to run across units where the run time is listed at 30 min., but they fold after just a few seconds.  The older units don't seem to "self calibrate" very well.

Over the past few months I've tested and calibrated close to 50 UPS units, and here is what I've found.  Even with the short switch to battery power during a self-test, it's not uncommon for the battery % to drop 10-20%.  In this range, there doesn't seem to be any major change in runtime after doing a full runtime calibration.  In fact, some have shown an increase in runtime after calibration. But when that drop is in the 20-30%, the runtime will decrease dramatically.

I just ran a runtime calibration on a unit that was dropping to 69% on the self-test, and it was showing 66 min of runtime.  When I ran the calibration, it dropped to 38% within the first minute, and then ran for about 10 minutes before the calibration completed.  I think the calibration cuts off at around 20-25%.  So, as you can see, the discharge curve is no where close to linier.  NEXT MORNING:  The listed runtime has dropped to 26 minutes.

Just my experience.  YMMV

See Answer In Context

Reply
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:27 AM

0 Likes
0
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:27 AM

This reply was originally posted by Bill on APC forums on 7/14/2014


Hi,

The runtime is dependent on the age of the battery/s and the amount of times the battery has discharged / been in use. The UPS will calibrate when it switches to on battery. What is the exact model Smart-UPS 3000? How old is the battery/s and does the UPS switch to battery often?  With that information we can review the online runtime chat to see if the UPS is within specs.

Reply
Battman_apc
Commander Battman_apc
Commander

Posted: ‎2021-06-29 08:27 AM

0 Likes
0
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:27 AM

This was originally posted on APC forums on 7/14/2014


What happens to the battery charge % readings in the first 5 to 30 or so seconds of when a UPS first goes to battery is not usually indicative of what will happen long term. Depending on load and battery age/health there is usually an initial drop in the first few seconds (that can sometimes be quite large),then sometimes what follows will be a short rebound (batt charge % & run time reported will increase very slightly/briefly), then it will drop steadily/slowly at a fairly even rate until low battery conditions are reached. All of this is governed by what has been termed the "coup de fouet" effect.

That there is sometimes a rebound is somewhat surprising to most people, and it comes in handy if you have a discharged (but not totally dead) car battery (eg left your lights on) if the battery can just crank the engine but not quite start it, turn everything off and wait about 5 to 10 mins then try again it may crank stronger and get the engine started.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:27 AM

0 Likes
0
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:27 AM

This reply was originally posted by Mark on APC forums on 7/14/2014


Thanks Bill, this battery was installed on January this year and looking at the logs this is the only time it's been running on battery other than it's initial calibration:

01/14/201406:26:16UPS: Runtime calibration passed via internal operation.
01/14/201406:01:02UPS: Started a runtime calibration.

How do I find the exact model?  SNMP just says:

.1.3.6.1.4.1.318.1.1.1.1.1.1.0 = STRING: "Smart-UPS 3000"

Reply
Battman_apc
Commander Battman_apc
Commander

Posted: ‎2021-06-29 08:27 AM

0 Likes
0
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:27 AM

This was originally posted on APC forums on 7/14/2014


Back panel of the UPS should have a Model / Serial No Sticker.

Reply
roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-29 08:28 AM

0 Likes
0
487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:28 AM

This was originally posted on APC forums on 7/17/2014


I deal with a large number of UPS units in locations across the US.  Over the past few months I have been dealing with some VERY old UPS units and also some VERY old batteries.  Some of the UPS units were installed in the mid to late 90"s and a few more in the early 2000's.  By far, the majority of our units are from 2006-2007.  Some of the batteries in those units have never been replaced.  We have started to run across units where the run time is listed at 30 min., but they fold after just a few seconds.  The older units don't seem to "self calibrate" very well.

Over the past few months I've tested and calibrated close to 50 UPS units, and here is what I've found.  Even with the short switch to battery power during a self-test, it's not uncommon for the battery % to drop 10-20%.  In this range, there doesn't seem to be any major change in runtime after doing a full runtime calibration.  In fact, some have shown an increase in runtime after calibration. But when that drop is in the 20-30%, the runtime will decrease dramatically.

I just ran a runtime calibration on a unit that was dropping to 69% on the self-test, and it was showing 66 min of runtime.  When I ran the calibration, it dropped to 38% within the first minute, and then ran for about 10 minutes before the calibration completed.  I think the calibration cuts off at around 20-25%.  So, as you can see, the discharge curve is no where close to linier.  NEXT MORNING:  The listed runtime has dropped to 26 minutes.

Just my experience.  YMMV

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc