Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
I just purchased two used Smart-UPS 1400s, which utilize a serial connection. When I connect the serial cable to my server, then plug it into the UPS, it immediately kills the power to the UPS and thus, my server.
I assumed they use a standard db9 RS232 connection. Is that not right?
I tried this with and without having PowerChute installed. It made no difference.
When the serial cable was attached at both ends, I could not even turn the UPS on. I had to disconnect the cable from the UPS in order to power everything back up.
Any advice and insight would be much appreciated.
tia.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Hey,
You need to use the cable shipped with the UPS. Its part number should be 940-0024C or 940-0024D, or 940-1524C or 940-1524D , this depends on what specific UPS model you are using.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Thanks for the reply.
As I purchased them used, they didn't come with cables. I'll see if I can find some.
Todd.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:09 AM . Last Modified: 2024-03-08 01:29 AM
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.