Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84260members
353366posts

Shutdown on Runtime Calibration?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
dreamcatcher_apc
Crewman
Crewman
0 Likes
4
579

Shutdown on Runtime Calibration?

This was originally posted on APC forums on 2/27/2013


Context:

We never performed a runtime calibration on our Smart-UPS. So we're new on that action. After replacing two UPS we want to perform a runtime calibration via PowerChute Business Edition. There are 8 servers attached and shutdown sequence is configured to shutdown these servers (7 via shutdown script triggered via PowerChute and 1 directly by that software).

Question:

If we perform runtime calibration via PowerChute Business Edition will the configured shutdown sequence be triggered or not? We assume, no shutdown sequence will be triggered. Correct?

Thanks for your answers!


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
579

Re: Shutdown on Runtime Calibration?

This reply was originally posted by Angela on APC forums on 2/27/2013


You're right - runtime calibrations issued via software should only discharge the UPS to between 10-20% and not turn the UPS off.

See Answer In Context

BillP
Administrator Administrator
Administrator
0 Likes
0
579

Re: Shutdown on Runtime Calibration?

This reply was originally posted by Angela on APC forums on 3/4/2013


Oh sorry, no, it will not execute your script. This is not treated as a shutdown or on battery event.

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
580

Re: Shutdown on Runtime Calibration?

This reply was originally posted by Angela on APC forums on 2/27/2013


You're right - runtime calibrations issued via software should only discharge the UPS to between 10-20% and not turn the UPS off.

dreamcatcher_apc
Crewman
Crewman
0 Likes
0
579

Re: Shutdown on Runtime Calibration?

This was originally posted on APC forums on 3/4/2013


Sorry, but the meaning of shutdown sequence was concerning the shutdown script and not the UPS here. So will the script get triggered via software calibration (and we have to disable it) or not?

Thank you,

Sebastian

BillP
Administrator Administrator
Administrator
0 Likes
0
580

Re: Shutdown on Runtime Calibration?

This reply was originally posted by Angela on APC forums on 3/4/2013


Oh sorry, no, it will not execute your script. This is not treated as a shutdown or on battery event.

dreamcatcher_apc
Crewman
Crewman
0 Likes
0
579

Re: Shutdown on Runtime Calibration?

This was originally posted on APC forums on 3/25/2013


Thanks for your, and sorry for my late response. I successfully performed a runtime calibration without any shutdown.