Servers not starting up automatically after power restore
APC UPS Data Center & Enterprise Solutions Forum
Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.
Solved
MKMaduro_apc
Ensign
Ensign
179
This was originally posted on APC forums on 12/7/2015
I have two servers who are connected to two different APC Smart-ups. Problem that I have is that neither server starts automatically after power restore when a power failure has happen.
Can someone tell me what I am doing wrong that the servers does not start automatically after power restore?
Servers
Connected to UPS
HP Proliant ML370 G5
APC Smart-UPS 2200
HP Proliant ML350p Gen8
APC Smart-UPS 1500
Basic settings both UPS
Time required for shutdown sequence
12 minutes
Low battery signal
8 minutes
OS shutdown duration
10:30 minutes
OS shutdown type
shutdown
Enable OS reboot
Yes
UPS turn on battery capacity
30%
UPS turn on delay
1 minutes
Thanks
Accepted Solutions
BillP
Administrator Administrator
Administrator
Re: Servers not starting up automatically after power restore
This reply was originally posted by Bill on APC forums on 12/7/2015
Hi,
You need to set OS to turn on when AC is restored in the BIOS of the computers. We have Kbase FA159550 "Computer will not automatically reboot after UPS has shutdown and restarted" that should help with this issue.
See Answer In Context
1 Reply 1
BillP
Administrator
Hi,