Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Send a sms.

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Send a sms.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Pietrick_apc
Ensign Pietrick_apc
Ensign

Posted: ‎2021-06-29 06:00 AM

0 Likes
7
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

Send a sms.

This was originally posted on APC forums on 1/24/2017


Is it possible to send a sms with a smart-ups?

I need to make a project for school, and my project is to try send a sms with a smart-ups when he goes on battery.  

Thanks,

Pietrick.

EDIT: 24-01-2017 (13:54)

I do have another question, if i want to send a mail with Powerchute business (when power fail) do i need a Network Management Card?  

(sorry i am kinda beginner with UPS things.)

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • send
  • smart
  • sms
  • ups
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This reply was originally posted by Haseeb on APC forums on 1/24/2017


Hello Pietrick

1) To answer your first question, "sms with a smart-ups".

Unfortunately, there is no way to send an SMS for UPS based events, regardless of what Network Management Card you have or UPS for that matter.  However, an alternative method for utilizing SMS notification, is to purchase Schneider Electric remote monitoring service (RMS).  In using this service, the UPS Network Management Card 1 uses emails to send to our RMS team who then can alert customer (via email or SMS).  The UPS Network Management Card 2 sends the information out via HTTP.  The RMS team can view the UPS information on their web portal and alert customer (via email or SMS).  However I doubt that you would be interested in the RMS service, especially since you only have a school project.  An alternative solution would be to use the following smart slot card that you can purchase for your UPS (if it does not already have one).

Dry Contact I/O SmartSlot Card (AP9613): http://www.apc.com/shop/ie/en/products/Dry-Contact-I-O-SmartSlot-Card/P-AP9613?isCurrentSite=true

Installation and Configuration Manual for AP9613: http://www.apc.com/salestools/PMAR-8XZJ9Y/PMAR-8XZJ9Y_R2_EN.pdf

With this card, you configure the UPS events (such as on battery) to trigger an output relay on the smart card.  Once you get the relay triggered, you can then use that as a signal to drive an external GSM Modem (third party device).  From this point on, the GSM modem will take care of sending out the SMS.  You can find many school based projects for designing embedded GSM modem based control applications (Google is your friend).

2) To answer your second question regarding Powerchute business.

The POWERCHUTE PERSONAL EDITION (requires USB connection only) and the POWERCHUTE BUSINESS EDITION requires either a USB or serial cable connection.  Both editions do 'not' require an NMC.  POWERCHUTE BUSINESS EDITION will send out emails over the LAN from the computer on which it is installed.

I hope the above information helps.

Kind Regards

See Answer In Context

Reply
Share
Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This reply was originally posted by Haseeb on APC forums on 1/24/2017


Hello Pietrick

1) To answer your first question, "sms with a smart-ups".

Unfortunately, there is no way to send an SMS for UPS based events, regardless of what Network Management Card you have or UPS for that matter.  However, an alternative method for utilizing SMS notification, is to purchase Schneider Electric remote monitoring service (RMS).  In using this service, the UPS Network Management Card 1 uses emails to send to our RMS team who then can alert customer (via email or SMS).  The UPS Network Management Card 2 sends the information out via HTTP.  The RMS team can view the UPS information on their web portal and alert customer (via email or SMS).  However I doubt that you would be interested in the RMS service, especially since you only have a school project.  An alternative solution would be to use the following smart slot card that you can purchase for your UPS (if it does not already have one).

Dry Contact I/O SmartSlot Card (AP9613): http://www.apc.com/shop/ie/en/products/Dry-Contact-I-O-SmartSlot-Card/P-AP9613?isCurrentSite=true

Installation and Configuration Manual for AP9613: http://www.apc.com/salestools/PMAR-8XZJ9Y/PMAR-8XZJ9Y_R2_EN.pdf

With this card, you configure the UPS events (such as on battery) to trigger an output relay on the smart card.  Once you get the relay triggered, you can then use that as a signal to drive an external GSM Modem (third party device).  From this point on, the GSM modem will take care of sending out the SMS.  You can find many school based projects for designing embedded GSM modem based control applications (Google is your friend).

2) To answer your second question regarding Powerchute business.

The POWERCHUTE PERSONAL EDITION (requires USB connection only) and the POWERCHUTE BUSINESS EDITION requires either a USB or serial cable connection.  Both editions do 'not' require an NMC.  POWERCHUTE BUSINESS EDITION will send out emails over the LAN from the computer on which it is installed.

I hope the above information helps.

Kind Regards

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This was originally posted on APC forums on 1/24/2017


If you have network connectivity, you could try emailing the email-to-SMS gateway for your wireless carrier:

http://mfitzp.io/list-of-email-to-sms-gateways/

Reply
Share
Pietrick_apc
Ensign Pietrick_apc
Ensign

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This was originally posted on APC forums on 1/25/2017


On 1/24/2017 5:43 PM, Haseeb said:

Hello Pietrick

1) To answer your first question, "sms with a smart-ups".

Unfortunately, there is no way to send an SMS for UPS based events, regardless of what Network Management Card you have or UPS for that matter.  However, an alternative method for utilizing SMS notification, is to purchase Schneider Electric remote monitoring service (RMS).  In using this service, the UPS Network Management Card 1 uses emails to send to our RMS team who then can alert customer (via email or SMS).  The UPS Network Management Card 2 sends the information out via HTTP.  The RMS team can view the UPS information on their web portal and alert customer (via email or SMS).  However I doubt that you would be interested in the RMS service, especially since you only have a school project.  An alternative solution would be to use the following smart slot card that you can purchase for your UPS (if it does not already have one).

Dry Contact I/O SmartSlot Card (AP9613): http://www.apc.com/shop/ie/en/products/Dry-Contact-I-O-SmartSlot-Card/P-AP9613?isCurrentSite=true

Installation and Configuration Manual for AP9613: http://www.apc.com/salestools/PMAR-8XZJ9Y/PMAR-8XZJ9Y_R2_EN.pdf

With this card, you configure the UPS events (such as on battery) to trigger an output relay on the smart card.  Once you get the relay triggered, you can then use that as a signal to drive an external GSM Modem (third party device).  From this point on, the GSM modem will take care of sending out the SMS.  You can find many school based projects for designing embedded GSM modem based control applications (Google is your friend).

2) To answer your second question regarding Powerchute business.

The POWERCHUTE PERSONAL EDITION (requires USB connection only) and the POWERCHUTE BUSINESS EDITION requires either a USB or serial cable connection.  Both editions do 'not' require an NMC.  POWERCHUTE BUSINESS EDITION will send out emails over the LAN from the computer on which it is installed.

I hope the above information helps.

Kind Regards

Haseeb,

Thanks allot for your help, now i got allot more options/way's to go. I am not sure which option i should do. Ill search today for the best one. After my school project they keep running the system(if i finished  it). 

Thanks,

Pietrick

Reply
Share
Pietrick_apc
Ensign Pietrick_apc
Ensign

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This was originally posted on APC forums on 1/25/2017


On 1/24/2017 8:33 PM, voidstar said:

If you have network connectivity, you could try emailing the email-to-SMS gateway for your wireless carrier:

http://mfitzp.io/list-of-email-to-sms-gateways/

Voidstar,

I searched for that, the problem is in the Netherlands most of providers do not support it. And the provider we use doesn't support it as well.

Still thanks you wanted to help me out!

Pietrick 

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This was originally posted on APC forums on 1/25/2017


That's too bad! You might have already tried this but one way to find the SMS gateway is to use your phone to send an SMS to your email address. Otherwise, often people use Twilio to send SMSes, however that will require some plumbing work on your end. Perhaps curl or wget to POST to their REST API using PowerChute's command file option.

One thing to be aware of is when power goes out, does your internet work?

Some other options:

1) AP9635 card has a modem and can dial a number when an event occurs. Rather expensive and I don't think there's a lot of support for this because not many people use it.

2) Simple signaling includes an AC Fail signal. Might be a cheaper way of interfacing the UPS with custom GSM hardware suggested by Haseeb. I suspect a GSM module will need less ongoing support from you than an internet service after your project is over.

Reply
Share
Pietrick_apc
Ensign Pietrick_apc
Ensign

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This was originally posted on APC forums on 1/25/2017


On 1/25/2017 9:48 AM, voidstar said:

Perhaps curl or wget to POST to their REST API using PowerChute's command file option.

When i want to use curl i need a linux device  connected to the ups rigth?

I really  appreciate that you want to help me out !

Reply
Share
Pietrick_apc
Ensign Pietrick_apc
Ensign

Posted: ‎2021-06-29 06:00 AM

0 Likes
0
811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 06:00 AM

This was originally posted on APC forums on 1/25/2017


I got it. I just configured the mail give smtp acces in sb2011 and then he send a mail.

I needed to send a text so use messagebird to make from a mail a sms.

Thanks for your help !

Pietrick

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc