Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82561members
350171posts

Self Test Scheduling

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
killdoser4_apc
Cadet
0 Likes
3
282

Self Test Scheduling

This was originally posted on APC forums on 5/12/2014


Hey everyone,

We have a few UPS units and I found where to set them to run a self test every 7 or 14 days etc. I was wondering if there was any way to configure the schedule to not run self tests on the weekends and just let it run one during the work week. From what I can see there is no way to set that but I needed conformation just to be sure.

Thanks in advance

Tags (2)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
282

Re: Self Test Scheduling

This reply was originally posted by Angela on APC forums on 5/12/2014


You're right - you cannot configure the automatic/scheduled self test on most, if not all UPS models. It will happen based on the time you first turned the UPS. So, to avoid weekends, you'd have to perhaps reboot the UPS during the week day to get it to reset the timing on the automatic self test.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
282

Re: Self Test Scheduling

This reply was originally posted by Matt on APC forums on 7/10/2014


Don't most UPSs count the 14 day interval based on when the last self test is run (whether manually commanded or automatic)? Therefore, if you wanted the self test to run on Saturday mornings, command it to perform one next Saturday morning. It should reset its internal time counter and attempt the next "Scheduled" self test 14 days later... on Saturday morning. Keep in mind the timers in these UPSs are not exactly perfect, so you will see some creep in the exact self test hour/minute as the months progress.

BillP
Administrator Administrator
Administrator
0 Likes
0
282

Re: Self Test Scheduling

This reply was originally posted by Bill on APC forums on 7/11/2014


Joe,

to answer your question "Don't most UPSs count the 14 day interval based on when the last self test is run (whether manually commanded or automatic)?" No. The self-test timer will not be affected by a manual self-test. It always stays with the 14 days since the last boot up.

BillP
Administrator Administrator
Administrator
0 Likes
0
283

Re: Self Test Scheduling

This reply was originally posted by Angela on APC forums on 5/12/2014


You're right - you cannot configure the automatic/scheduled self test on most, if not all UPS models. It will happen based on the time you first turned the UPS. So, to avoid weekends, you'd have to perhaps reboot the UPS during the week day to get it to reset the timing on the automatic self test.