Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
I have a UPS SURTD5000XLI which stopped with LEDs flashing like this:
Fault LED + 1st and 2nd Battery LED from top to bottom
Does anyboby know the meaning of these error codes?
I really appreciate your help
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Joe,
The fault code means Logic Power Supply Fault. Did the UPS dropped the load as well? Have you tried turning the UPS off/on?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Yes, it dropped the load. I tried off/on several times but nothing changed. Even if i set it in bypass mode the result is the same.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Joe,
The fault code means Logic Power Supply Fault. Did the UPS dropped the load as well? Have you tried turning the UPS off/on?