84705members
354089posts
SURTA1500XL with SURTA48XLBP moved... problems.
30media_apc
295
This was originally posted on APC forums on 5/28/2012
We moved a SURTA1500XL with SURTA48XLBP and now it won't turn back on. It keeps on chirping and the fault light and the top two battery charge LED's are flashing. Tried communicating with server but it won't see it. The wiring fault LED is not illuminated. It won't turn on at all without the 48XL plugged into the back. Any ideas?
30media_apc
Re: SURTA1500XL with SURTA48XLBP moved... problems.
This was originally posted on APC forums on 5/29/2012
I removed the batteries, and one of the batteries in the expansion unit was bulging. I was luckily able to remove it, barely, but the unit won't power up at all. I disconnected the expansion unit and the 1500 won't power up at all. I haven't checked battery voltages as of yet, but I'm wondering with the battery bulging if there isn't something else awry, preventing the unit from working at all. I'm going to have the batteries disposed and I will order new ones... unless you think there might be more damage than just dead batteries.
4 Replies 4
This reply was originally posted by Dakota on APC forums on 6/12/2012
Just to add when the batteries go bad these smart upses will go some goofy stuff
My SU1000RM2U did this when the batteries died:
https://www.youtube.com/watch?v=mJtEBVde9LM
This reply was originally posted by Chris on APC forums on 5/29/2012
Moving a UPS wouldn't usually cause this problem assuming of course it wasn't damaged or left unplugged for several days. When you say the UPS won't turn on without the XL bp connected, do you mean if you try to turn on the UPS without it, it won't turn on at all and when you connect it, it turns on with this fault? If so, you may want to check the batteries and make sure they are seated properly(on the UPS). If everything checks out, it may be a bigger issue and I would suggest calling tech support.
30media_apc
I just found out that the UPS was left unplugged for several days... I didn't realize that until today. And, yes, when the bp is unplugged it won't turn on at all, and then when I plug it in it goes to fault. Should I order replacement batteries, or do you think it is more than just dead batteries?
30media_apc