Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SURT6000XLI - Error messages - please help
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:20 AM. Last Modified: 2024-03-1802:28 AM
SURT6000XLI - Error messages - please help
Hello,
we are using an APC SURT6000XLI with 4 extra battery packs SURT192XLBP. A few years it was working really fine. But now I have found some entries in the logs I do not understand, maybe somebody can tell me, what to do:
03:55:15 UPS: In bypass in response to an internal hardware fault.
03:55:17 UPS: An inverter fault exists.
03:55:20 UPS: Refused a self-test; UPS is overloaded.
The batteries are ~ 6 years old. Is the reason for this error messages, that I have to replace them?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:20 AM. Last Modified: 2024-03-1802:28 AM
Hi Digger -
These faults indicate a possible hardware fault with the UPS itself, not the batteries. Did the faults clear by themselves? If not, you can try clearing them with e "Brain Dead" procedure. To do this:
Turn Off the UPS
Unplug the UPS from Utility power
Disconnect all batteries internal and external
Reconnect batteries, reconnect utility power, and turn UPS back on
If this does not clear your error you likely have a hardware fault. I would contact your local tech support team for further assistance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:20 AM. Last Modified: 2024-03-1802:28 AM
Hi Digger -
These faults indicate a possible hardware fault with the UPS itself, not the batteries. Did the faults clear by themselves? If not, you can try clearing them with e "Brain Dead" procedure. To do this:
Turn Off the UPS
Unplug the UPS from Utility power
Disconnect all batteries internal and external
Reconnect batteries, reconnect utility power, and turn UPS back on
If this does not clear your error you likely have a hardware fault. I would contact your local tech support team for further assistance.
Thanks!
Liam