SURT10000XLI fault and bypass LED together

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
3
527

SURT10000XLI fault and bypass LED together

This question was originally posted by Omar on APC forums on 1/4/2016


I have and issue with APC UPS , the bypass led and fault led are together the battery led like

0

1

0

1

0

which 0 is off and 1 is green light , 

please advice . 

Attachments
Tags (4)

Accepted Solutions
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
527

Re: SURT10000XLI fault and bypass LED together

This was originally posted on APC forums on 1/5/2016


Hi Omar,

It is a possibility that the batteries are bad. However, I can not guarantee that replacing the batteries will fix the issue. We can take the voltage of the batteries using a volt meter. You can just check the status of each pack by testing it at the Anderson connector. When they are fully charged they should be about 110 volts. LEt me know what you get. 

See Answer In Context

3 Replies 3
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
527

Re: SURT10000XLI fault and bypass LED together

This was originally posted on APC forums on 1/4/2016


Hi Omar,

This decodes to  a battery charger fault. This could either be bad batteries or a malfunction in the charging mechanism. Do you know how old the batteries are? Do you have batteries from a similar unit that we can borrow to see if the batteries are the culprit? 

BillP
Administrator Administrator
Administrator
0 Likes
0
528

Re: SURT10000XLI fault and bypass LED together

This reply was originally posted by Omar on APC forums on 1/4/2016


It is from 2011 or 2012 i don't know exactly.  Unfortunately I don't have any extra batteries to test  do you think that i have to change the batteries?

mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
528

Re: SURT10000XLI fault and bypass LED together

This was originally posted on APC forums on 1/5/2016


Hi Omar,

It is a possibility that the batteries are bad. However, I can not guarantee that replacing the batteries will fix the issue. We can take the voltage of the batteries using a volt meter. You can just check the status of each pack by testing it at the Anderson connector. When they are fully charged they should be about 110 volts. LEt me know what you get.