SRT10KXLI does not show vmax or vmin for input voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
knowlesy_apc
Ensign
Ensign
0 Likes
8
460

SRT10KXLI does not show vmax or vmin for input voltage

This was originally posted on APC forums on 6/3/2015


Hi I have 2 x SRT10KXLI and on both the vmax and vmin dont show in data view ? Now I know it is sensing input (well I hope it is) as I can see it on its screen, am I missing somthing in the config or do I need to update ? 

Model: Smart-UPS SRT 10000
SKU: SRT10KXLI
Firmware Revision: UPS 02.1 (ID1002)
Manufacture Date: 09/21/2014

Model: Smart-UPS SRT 10000
SKU: SRT10KXLI
Firmware Revision: UPS 02.1 (ID1002)
Manufacture Date: 11/10/2014


Accepted Solutions
knowlesy_apc
Ensign
Ensign
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This was originally posted on APC forums on 8/19/2015


Hi, upgrading the firmware to the latest version fixed the issue

See Answer In Context

8 Replies 8
BillP
Administrator Administrator
Administrator
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This reply was originally posted by Jordan on APC forums on 6/3/2015


P,

Could you attach your data logs so that we could see them.  Screenshots would also help.

knowlesy_apc
Ensign
Ensign
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This was originally posted on APC forums on 6/4/2015


Hi Please see the attached photo and logs

Thanks

Attachments
Terry_Kennedy_apc
Commander
Commander
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This was originally posted on APC forums on 6/4/2015


The only thing I can think of is that your UPSs are a year newer than the software running on the management card, so you might want to try updating the management card's firmware. 6.2.1 is the latest at present and can be downloaded here.

It is also possible that this model of UPS doesn't provide that data to the management card, but I'd suggest updating the card firmware first.

knowlesy_apc
Ensign
Ensign
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This was originally posted on APC forums on 6/4/2015


It looks like it can read it from the status page see attached. I will set away the upgrade this afternoon.

Thanks

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This reply was originally posted by Jordan on APC forums on 6/4/2015


I would also recommend ensuring you having you have the latest NMC software for your unit - it would appear a reporting issue since on certain screens the input voltages are reported.  If this does not resolve the issue, I would recommend rebooting the web interface, possibly braindeading the unit if you have downtime, and contacting your local support because this is an international unit.

Regards,

knowlesy_apc
Ensign
Ensign
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This was originally posted on APC forums on 6/4/2015


Hi can you confirm what a few things are / mean ? 

  • NMC Software ?
  • braindeading the unit  ?

Thanks

 

BillP
Administrator Administrator
Administrator
0 Likes
0
460

Re: SRT10KXLI does not show vmax or vmin for input voltage

This reply was originally posted by Angela on APC forums on 6/9/2015


Hi P,

To me, it looks like your UPS output is off (even though there is AC input to the UPS). Though, it shows output voltage so that is strange.

Can you provide the full .tar dump from your UPS? Instructions here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

NMC software refers to the firmware version on the Network Management Card/interface in your UPS. This is currently v6.0.7 and you can update to v6.2.1 to see if anything changes. You can get it here -> http://www.apc.com/tools/download/index.cfm and look for Firmware Upgrades - UPS Network Management Card and look for SFSUMX621 to download. Instructions on upgrading are here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047 

Braindeading the unit refers to basically doing a communications reset on the unit. To do this, you'd need to remove/turn off anything plugged into the UPS and then turn off the UPS itself. Then, unplug/remove AC power from the UPS (so you could also flip the input breaker) and then holding down the off button on the front panel. On this UPS, you may also need to disconnect the battery modules and this discharges the UPS capacitors and resets the UPS internally.

I haven't seen this issue yet but I imagine it is something going on that we can address with some sort of update or reset.

knowlesy_apc
Ensign
Ensign
0 Likes
0
461

Re: SRT10KXLI does not show vmax or vmin for input voltage

This was originally posted on APC forums on 8/19/2015


Hi, upgrading the firmware to the latest version fixed the issue