Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

SNMP event triggers and Smart-UPS line

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: SNMP event triggers and Smart-UPS line
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
cernst_apc
Ensign cernst_apc
Ensign

Posted: ‎2021-06-28 09:30 PM

0 Likes
4
313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:30 PM

SNMP event triggers and Smart-UPS line

This was originally posted on APC forums on 3/10/2009


I'm working on developing some documentation on SNMP events. We use CA Unicenter TNG to receive traps, then hold them to a console for our NOC to watch over. I've got my ServerTech power strips figured out, now I'm on to the APC ups units.

I've downloaded the latest PowerNet MIB file (3.9.5) and looked at the defined events...good lord there are a lot. It appears that they've put all kinds of events in there that are for UPS units as well as other devices (xATSGeneratorVeryLowFuelLevelAlarmCleared).

Is there a way to determine which SNMP events are possible for a given Smart-UPS unit? I have a mix of SU700NET, SU700RM2U, SUA750RM2U, SUA750XL, SU700XL, and SUA3000XL units. In order to setup the filters, I need to know what will (or what I do not) want to be held on the message console.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
cernst_apc
Ensign cernst_apc
Ensign

Posted: ‎2021-06-28 09:30 PM

0 Likes
0
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:30 PM

This was originally posted on APC forums on 3/13/2009


The file did help, thank you.

The "Administration->Notification" section only works for a 9617. A 9606 has a different interface...but I'd imagine that even a 9605 will still send out the same traps a 9617 would.

I should have been clearer when talking about events/traps...I had meant for them to be the same thing, for every event, there is a trap.

If I allow all traps to be sent to the operator's "console", then a few things happen. I've noticed that some 9605 cards do not play nice with the "sua" series, and the card tends to reboot...I don't have this happen on "su" units. So if everything gets displayed, they'll be inundated with communications related messages. There might be a way to specifically block messages I don't want...that could be an option I'll work on.
As part of the project, I need to document what needs to happen when certain events occur...so knowing what events are sent will allow me to document as much as possible. If I don't, then I get a call...and I'm always on-call. We have a pretty good number of units out there, and the number grows.

APC UPS units are the only APC products I have networked.

Message was edited by: cernst

See Answer In Context

Reply
Share
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:30 PM

0 Likes
0
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:30 PM

This reply was originally posted by Anonymous on APC forums on 3/11/2009


Hi cernst,

Do you have Network Management Cards (NMC) in those UPS. The UPS themselves can not communicate over SNMP and will need an NMC to communicate on the network and enable the use of SNMP. Assuming you do have NMC's then you can use a program like Getif to do a mib walk on the UPS to see what information is available on that model. From there you can look through what is available and decide on what traps you want to monitor. Also in the NMC you will want to remember to set the IP of the trap receiver.

Is that what you were looking for?

Reply
Share
cernst_apc
Ensign cernst_apc
Ensign

Posted: ‎2021-06-28 09:30 PM

0 Likes
0
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:30 PM

This was originally posted on APC forums on 3/11/2009


yeah, I've got 9605's, 9606's, and 9617s.

doing a walk will only produce data on objects the UPS utilizes, but will not reveal what traps are used by the UPS. If you look at the PowerNet mib file, you have "products", "apcmgmt", and "SNMPv1 TRAPs" as the top three trees. If you expand the last option, it shows all the traps that the MIB file defines, but that doesn't mean the UPS can use them all.

A good example of a trap that may or may not be used, is the "baseFanFailure" trap. I have su700net boxes out there w/ 9605 cards. I also have sua3000xl units with 9617 cards. I don't know if either of the units will send out this trap. Some units do have fans...some do not.

APC traps are not very user friendly as they do not pass any data to the NMS. Each trap only has one object (mtrapargsString), which the value changes depending on the event. If they did pass data back, then I could do a walk to see if the UPS provides data for the included data object; if the object doesn't appear from a walk, then a good chance said trap would not be used by the unit. However, all we get to work with is an event with one object that responds with one static string dependent on the type of event.

Events that deal with temperature may work with UPS units and it may work with networked power strips.

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 09:30 PM

0 Likes
0
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:30 PM

This was originally posted on APC forums on 3/12/2009


On the web interface of your AP9606 and AP9617 cards with AOS 3xx, go to Administration->Notification

Almost all of the events listed there should have a corresponding trap, unless we've messed up. To get you started, I've compiled what I believe to be a list of all of the UPS related events and their trap #. It's attached to this message. I didn't include system traps. Like you said, any given UPS may not produce all of these traps, but each trap can be triggered by at least one UPS we've produced.

That said, you may want to rethink your approach. If you configure the NMS to log all traps coming from an APC device rather than specific traps, then you won't have to worry about entering new traps every time the firmware is updated or you add a new type of device to your network.

In addition, while most UPS traps attach mtrapargsString with the event text, other APC products differ. Check the PowerNET MIB for details.

I know this isn't everything you were looking for, but I hope this helps.

Attachments
Reply
Share
cernst_apc
Ensign cernst_apc
Ensign

Posted: ‎2021-06-28 09:30 PM

0 Likes
0
313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-28 09:30 PM

This was originally posted on APC forums on 3/13/2009


The file did help, thank you.

The "Administration->Notification" section only works for a 9617. A 9606 has a different interface...but I'd imagine that even a 9605 will still send out the same traps a 9617 would.

I should have been clearer when talking about events/traps...I had meant for them to be the same thing, for every event, there is a trap.

If I allow all traps to be sent to the operator's "console", then a few things happen. I've noticed that some 9605 cards do not play nice with the "sua" series, and the card tends to reboot...I don't have this happen on "su" units. So if everything gets displayed, they'll be inundated with communications related messages. There might be a way to specifically block messages I don't want...that could be an option I'll work on.
As part of the project, I need to document what needs to happen when certain events occur...so knowing what events are sent will allow me to document as much as possible. If I don't, then I get a call...and I'm always on-call. We have a pretty good number of units out there, and the number grows.

APC UPS units are the only APC products I have networked.

Message was edited by: cernst

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc