SMT750i don't want to go online

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
dynek_apc
Cadet
0 Likes
4
200

SMT750i don't want to go online

This was originally posted on APC forums on 3/26/2014


Hello All,

Few months back I bought a SMT750i and it worked just fine until today.

Today I noticed that no LED on the front were on so I started checking the menus and actually everything says 0% (Load: 0%, Batt: 0%), UPS Model is empty, etc.

If I unplug power, it makes a weird noise (don't remember it was making so much noise) but current remains available for devices plugged in.

I tried pushing the on/off button several times. I tried to push it for severals seconds (until 30sec) but nothing helps.

Any idea ?

Thank you


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
200

Re: SMT750i don't want to go online

This reply was originally posted by Bill on APC forums on 3/27/2014


Hi,

You can reset the Smart-UPS  by

1) Turn off all attached equipment

2) Turn off the UPS

3) Unplug UPS from wall

4) Disconnect Battery

5) You may hear an audible "click" from the UPS.

6) Reconnect battery, Plug UPS in, turn UPS on


See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
200

Re: SMT750i don't want to go online

This reply was originally posted by Angela on APC forums on 3/27/2014


What options to see you available in the Control menu on the front panel LCD?

Referring to this picture, all four LEDs are still off? The ones right below the power button? And when they are all off, your attached equipment still receives power?

2276_9A34F5BF04E80C8F8525761700678F53_MMAE_7V3Q7V_f_h_500x500.jpg

dynek_apc
Cadet
0 Likes
0
200

Re: SMT750i don't want to go online

This was originally posted on APC forums on 3/27/2014


Hello and thank you for your answer,

All LEDs are off, see picture I took. My equipment still receive power and if I simulate a power outage, I can hear the battery take over and it starts beeping as usual when power drops.

Anything special you want me to check in the menus ?

For instance if i try to run a Self Test, it says "Only in online".

Is there a way to force a complete shutdown / reboot ?

Thank you

2274_IMG_5437.jpg

BillP
Administrator Administrator
Administrator
0 Likes
0
201

Re: SMT750i don't want to go online

This reply was originally posted by Bill on APC forums on 3/27/2014


Hi,

You can reset the Smart-UPS  by

1) Turn off all attached equipment

2) Turn off the UPS

3) Unplug UPS from wall

4) Disconnect Battery

5) You may hear an audible "click" from the UPS.

6) Reconnect battery, Plug UPS in, turn UPS on


dynek_apc
Cadet
0 Likes
0
200

Re: SMT750i don't want to go online

This was originally posted on APC forums on 3/27/2014


Fantastic! It took a while cause it's kinda stuck in a rack but I was able to take it out unplug the rear thing that makes battery go live and it came back to normal state!

Thanks!