SMT3000RM2U how do I connect serial cable to manually power on and off?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
4
745

SMT3000RM2U how do I connect serial cable to manually power on and off?

This question was originally posted by Charles on APC forums on 3/22/2017


Hi everyone,

I'm looking to control (if possible) my SMT3000RM2U via the serial cable in terms of turning it on after a power failure and then when the utility power returns, to turn it off.

I found this post by Angela: http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/9407/turn-on-surt8000xl-remot...

which details pins 7,8 & 9 as being for this purpose, but the serial port on my SMT3000RM2U is RJ48 so I would like to know how to translate the above 7-8-9 connection to RJ48 connector.

Also- Angela mentions that the connection as a momentary (240ms) connection. What would the UPS do if the connection was constant in one state or the other (like a relay would create)?

Greatly appreciate your time!

Chuck

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
745

Re: SMT3000RM2U how do I connect serial cable to manually power on and off?

This reply was originally posted by Matt on APC forums on 8/29/2019


Hi Lilla

 

The cable required is actually a smart signalling cable APC part no. 940-0625A  rather than a generic serial cable.

 

Regards

 

Matt

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
745

Re: SMT3000RM2U how do I connect serial cable to manually power on and off?

This reply was originally posted by Liam on APC forums on 3/23/2017


Hi Charles - 

Next generation Smart-UPS (anything with an LCD screen) use a different communications protocol and cable pin-out than legacy products. You can get all the details in this application note: http://www.apc.com/salestools/MPAO-9E5RB5/MPAO-9E5RB5_R1_EN.pdf

Hope that helps,

Liam

BillP
Administrator Administrator
Administrator
0 Likes
0
745

Re: SMT3000RM2U how do I connect serial cable to manually power on and off?

This reply was originally posted by Charles on APC forums on 3/23/2017


Liam- Thank you! Exactly what I was looking for. Good day!

Charles

BillP
Administrator Administrator
Administrator
0 Likes
0
745

Re: SMT3000RM2U how do I connect serial cable to manually power on and off?

This reply was originally posted by Lilla on APC forums on 8/28/2019


Hi...in my case after replacing the batteries, the unit works fine, except for one thing. Whenever I plug in a Serial Data Cable into the back of the unit, and THEN plug it into a Serial Port, the UPS shuts down, or it simply will not start. With just the cable plugged into the UPS, and the other end unplugged, it runs or starts fine. I even tried a Serial to USB Adapter, and the same thing happens. I just bought a generic Serial Cable, and not this one, since it appears to be just a generic cable.

 

printed circuit board

BillP
Administrator Administrator
Administrator
0 Likes
0
746

Re: SMT3000RM2U how do I connect serial cable to manually power on and off?

This reply was originally posted by Matt on APC forums on 8/29/2019


Hi Lilla

 

The cable required is actually a smart signalling cable APC part no. 940-0625A  rather than a generic serial cable.

 

Regards

 

Matt