Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84261members
353366posts

SMT1500RM2U : Unacceptable utility voltage rate of change

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
TM1_apc
Crewman
Crewman
0 Likes
1
1285

SMT1500RM2U : Unacceptable utility voltage rate of change

This was originally posted on APC forums on 4/13/2011


Hi,

The SMT1500RM2U UPS is working fine, but I noticed this message under the UPS Tab/Overview section: Last Battery Transfer: Unacceptable utility voltage rate of change.

I'm not quite sure what to make of that informational message. Can some one give me some facts on this?


Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
1285

Re: SMT1500RM2U : Unacceptable utility voltage rate of change

This reply was originally posted by Angela on APC forums on 4/13/2011


this generally means there was a rapid change in voltage and/or frequency sometimes. for instance, if a high current device turned on or drew a large amount of current, the voltage may have dropped down rapidly but then returned to 120v. thus, the UPS transferred to battery most likely cause of an issue with the input voltage.

you may also see it defined as delta V / delta T - desribing the rapid change if voltage over time.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
1286

Re: SMT1500RM2U : Unacceptable utility voltage rate of change

This reply was originally posted by Angela on APC forums on 4/13/2011


this generally means there was a rapid change in voltage and/or frequency sometimes. for instance, if a high current device turned on or drew a large amount of current, the voltage may have dropped down rapidly but then returned to 120v. thus, the UPS transferred to battery most likely cause of an issue with the input voltage.

you may also see it defined as delta V / delta T - desribing the rapid change if voltage over time.