Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
ocgltd_apc
Ensign
Ensign
0 Likes
3
293

Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

This was originally posted on APC forums on 6/7/2011


We had a lengthy power outage last night and the UPS ran out of battery power. When power returned (about 1 hr after restart) we started getting the error "Severe - UPS: Bypass not in range; either frequency or voltage." (I have a Symmetra 8000 with web card:)

Based on the manual I think I understand the error message. However, the ups event log does not show any over/under voltage or frequency. When I check the current state page of the web interface to the ups, it shows info below. Everything looks fine.

How do I know what the cause of the error is? (Volt or Freq). Is this recorded somewhere? What is the acceptable volt & freq range?

------------------------------

Reason For Last Transfer To Battery: Due to software command or UPS's test control.
Internal Temperature: 037.3 Degrees Celsius
Describes utility power status
Input Voltage: 237.3 VAC
Input Frequency: 59.99 Hz
Maximum Input Voltage: 237.3 VAC
Minimum Input Voltage: 235.6 VAC
Describes output power status
Output Voltage: 234.0 VAC
Output Frequency: 60.00 Hz
Output Current: 00.0 Amps
Output Watts at n+0: 010 %
Output Watts at n+0: 010 %
Output VA at n+0: 007 %
Output VA at n+0: 007 %
Fault tolerance parameters
Redundancy: n+0
Present kVA Capacity: 04.0 kVA
Describes battery status
Battery Capacity: 100.0 %
Runtime Remaining: 0180 Minutes
Nominal Battery Voltage: 120.0 VDC
Actual Battery Bus Voltage: 137.1 VDC
Number of Batteries: 002
Number of Bad Batteries: 000
Self-Test Result: Passed
Self-Test Date: 06/07/2011
Calibration Result: Passed
Calibration Date: 06/03/2011

Message was edited by: ocgltd

Message was edited by: ocgltd


Accepted Solutions
ocgltd_apc
Ensign
Ensign
0 Likes
0
293

Re: Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

This was originally posted on APC forums on 6/11/2011


I widened the freq range to +/ .3 (which MAY solve the problem - but I won't chase this further)
And I turned off drop load on bypass (which caused all my messages)

Thanks!

See Answer In Context

3 Replies 3
ocgltd_apc
Ensign
Ensign
0 Likes
0
293

Re: Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

This was originally posted on APC forums on 6/7/2011


A little more info. I checked the MIM status and see:

state=05 fan=0
100 10 00110101
Vint=244.2 00000000

So input voltage is correctly set to 240v (I think - and why would that change after a full discharge).

The Voltage status shows:

staus
00 Vin Vout Iout
1 237.3 234.0 00.0A

Hopefully there's another clue there for someone knowledgeable.

Thanks

ocgltd_apc
Ensign
Ensign
0 Likes
0
293

Re: Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

This was originally posted on APC forums on 6/9/2011


Here are the settings you asked for:

VoutReport set to AUTO
Output freq set to 60Hz +/- 0.1Hz
Bypass set to "Go to bypass" (was in Drop Load but I just changed it)

So now, how should I interpret these? Should I set VoutReport to 240v? (I have this unit on single phase 240v). Is the output freq too narrow? Does bypass setting matter? etc

I just replaced the SYMIM 2 weeks ago, after the last one died following a power outage. Could this be a factor?

I seem to recall that PowerChute produces a graph of Voltage over time, so I installed Powerchute Business Edition. But PowerChute isn't able to detect the UPS (connected by serial port). I think my Symmetra 8000 is not on the supported device list for Powerchute...is this worth pursuing or is this just incompatable?

Message was edited by: ocgltd

ocgltd_apc
Ensign
Ensign
0 Likes
0
294

Re: Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

This was originally posted on APC forums on 6/11/2011


I widened the freq range to +/ .3 (which MAY solve the problem - but I won't chase this further)
And I turned off drop load on bypass (which caused all my messages)

Thanks!