Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
RT10000XL The output power is turned off
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:31 PM. Last Modified: 2024-03-0610:54 PM
RT10000XL The output power is turned off
Hello,
I have a RT 10000XL with 7 battery packs. It performed a self check yesterday and reported fine.
Today, it just turned off the output power and I couldn't even access the web interface. I could ping the IP address, no LEDs were lit but the coolers were running.
After turning it off on the breaker and waiting for some time, It eventually turned on again with a battery fault indication.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:31 PM. Last Modified: 2024-03-0610:54 PM
Hi,
Please provide the event and data logs from the network card.
The information provided show that the UPS failed a self-test but most likely that test was run when the UPS started so would not be the cause of the drop. The information also shows that the batteries where in a discharged state momentarily. This could be caused by week batteries or the load. What is the load percentage?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:31 PM. Last Modified: 2024-03-0610:54 PM
Hi,
Please provide the event and data logs from the network card.
The information provided show that the UPS failed a self-test but most likely that test was run when the UPS started so would not be the cause of the drop. The information also shows that the batteries where in a discharged state momentarily. This could be caused by week batteries or the load. What is the load percentage?