RT 6000 RM XL and Cisco 3750E Switch in Japan

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • RT 6000 RM XL and Cisco 3750E Switch in Japan
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

0 Likes
2
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

RT 6000 RM XL and Cisco 3750E Switch in Japan

Hey everyone

We just changed our UPS in Tokyo from smart ups 3000 to a new Smart-UPS RT 6000 RM XL (SURTD6000RMXLJP3U)

All our equipment is working fine on the new UPS except our Cisco 3750 switches with C3KPWR1150WAC PSU's. For some reason they do not power up at all (AC LED is green, but PS LED is red) The required voltage for this power supply is 115V and I think the new UPS only delivers max 110?

I attached some screenshots of the web interface and the specs of the PSU in the Cisco Switch. Right now the switches are connected to the wall socket instead of the UPS and working fine.

Anyone have any idea how I can get this resolved? Can I get change the "Rated output voltage" as shown on picture 2? (Attached)

Everything was working fine with the old UPS.

Thanks!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

>
Anyone have any idea how I can get this resolved? Can I get change the "Rated output voltage" as shown on picture 2?
>

I'd certainly check to see if all the connected equipment is specified to accept 120V, and if so, try the 120/208 setting. For instance, 120V would be within the 115-240V range accepted by the Cisco switch.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

This ups is designed to output 100/200v as that is the voltage standard in Japan. Most equipment even in the 115v range can operate with 100v but if it cannot, unfortunately you may need a UPS or equipment that will work with Japan power.

Edit: Agree with below message. I didn't look at all the attachments. As long as all your equipment can handle 120, it would be best to switch to 120.

Message was edited by: Chrisri30

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

0 Likes
0
1067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:32 AM

>
Anyone have any idea how I can get this resolved? Can I get change the "Rated output voltage" as shown on picture 2?
>

I'd certainly check to see if all the connected equipment is specified to accept 120V, and if so, try the 120/208 setting. For instance, 120V would be within the 115-240V range accepted by the Cisco switch.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now