PowerChute network shutdown and power failure simulation

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
259

PowerChute network shutdown and power failure simulation

This question was originally posted by Philippe on APC forums on 5/30/2017


Hello, I realize the reconfiguration of a Smart-ups 5000 with a management card AP9630 (with sumx 6.4.6) and powerchute network shutdown. I added a test agent and I would like to simulate a power failure to verify that the powerchute configuration is operational before adding other agents.

Is there a way to do this simulation without disrupting the rest of the diet?

Thank you in advance.
Philippe

Tags (2)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
259

Re: PowerChute network shutdown and power failure simulation

This reply was originally posted by Bill on APC forums on 5/30/2017


Hi,

To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
260

Re: PowerChute network shutdown and power failure simulation

This reply was originally posted by Bill on APC forums on 5/30/2017


Hi,

To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS.