PowerChute is not receiving data from the Network Management Card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute is not receiving data from the Network Management Card
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Anonymous user
Not applicable

Posted: ‎2021-09-20 05:15 PM

0 Likes
5
3004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-20 05:15 PM

PowerChute is not receiving data from the Network Management Card

I'm having an issue getting an NMC2 to register with a powerchute esxi appliance. I had it working on one appliance two weeks ago, but the root credentials were not working, so I downed that one and deployed a new one. Registration fails on the new one, however.

 

This is on a SmartUPS 1000. I can access the NCM2 card fine. I've brain dead the thing, reset the NMC but for TCPIP and updated the firmware to v6.9.6, but no love.

 

I did contact APC support, spent an hour on a call, but they were not able to sort this out. They were supposed to get back to me, but never did. In the meantime, I've had two power outages at this site due to recent storms and have had to rebuild the BDR appliance once. Kind of need to get this sorted ASAP. PCNS error image included.

 

Thanks in advance.

 

 

PowerChute_Network_Shutdown.png

 

 

 

 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-09-24 11:28 AM

0 Likes
3
2984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-24 11:28 AM

@Anonymous user 

 

When you run the PowerChute Setup does PowerChute register an IP address with the NMC? 

What is the network information for both PowerChute appliance and the NMC? IP addresses, gateway, subnet mask.

Have you install netstat on the PowerChute appliance and if so does it show that UDP port 3052 is open?

To install netstat enter the command as root yum -y install net-tools 

Once netstat has been install run the command netstat -tulpa 

 

The output should look like below

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-09-27 09:54 AM . Last Modified: ‎2021-09-27 09:56 AM

In response to BillP
0 Likes
2
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-27 09:54 AM . Last Modified: ‎2021-09-27 09:56 AM

@BillP Thanks for the reply. Answers/comments below:

 

When you run the PowerChute Setup does PowerChute register an IP address with the NMC?  

-No, PCNS appliance setup fails during UPS registration (powerchute is not receiving data from NMC), which is what instigated this post. I did manually add the appliance ip address as a client via the NMC2 card, per that one support call I had with APC. It's still there. 

 

What is the network information for both PowerChute appliance and the NMC? IP addresses, gateway, subnet mask.

NMC2

IP: 172.16.10.25

GW: 172.16.10.1

SM: 255.255.255.0

 

PCNS Appliance

IP: 172.16.10.9/16

GW: 172.16.10.1

Since the appliance doesn't have a discreet subnetmask field on the CL network setup screen, i've alternately both the default /16 (255.255.0.0) and /24 (255.255.255.0) with the same result.

 

Regarding netstat. I've just installed it. Results below.

 

netstat.png

 

Additionally, as a test, I installed PCNS for Windows on one of my Windows Server VMs, and it was able to register the UPS. So the appliance on the same ESXI host fails to register the UPS while the Windows VM PCNS is able to. Thoughts on this?

 

Update for clarity.

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-10-01 12:03 PM

In response to Anonymous user
0 Likes
1
2940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-01 12:03 PM

@Anonymous user 

 

The subnet masks on the systems must match for communications. Another cause is if the network card has not been configured to allow PowerChute access. See Schneider Electric FAQ FA159624

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-10-03 07:47 AM

In response to BillP
0 Likes
0
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-03 07:47 AM

The subnet mask on. the appliance does match the network. Also, the appliance was listed as a powerchute client. So, not sure what there is left to check. Since I've yet to get a response from Schneider on my original ticket for an assist, we ended up purchasing another UPS with an NMC3. The appliance has no issue registering the new SMT1500. Network setting are the same as the NMC2 on the SMT1000 (beside the ip address, of course). Schneider's lack of direct follow-up on our support ticket is very disappointing. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Barliman_apc_customer
Ensign Barliman_apc_customer
Ensign

Posted: ‎2021-10-15 07:53 AM

0 Likes
0
2844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-15 07:53 AM

Have you verified the AuthPhrases, protocol, ID and PW  match on the NMC and in PowerChute?

Create a file something.ini with these lines

[PowerChute]

PCNSUsername = apc

AuthPhrase = My Auth Phrase

 

Upload to your NMC

 

Sign in to PowerChute and in Communications make sure the protocol matches the card, http vs https

In credentials(?) make sure username and PW match the NMC and for AuthPhrase type the same phrase as in the ini file you uploaded. Type the spaces too.

Restart powerchute. If windows, sc stop PCNS1 && sc start pcns1

 

check your pwrchute\group1\eventlog.txt

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of