PowerChute cannot locate the vCenter Server VM

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
bdownes_apc
Crewman
Crewman
0 Likes
1
193

PowerChute cannot locate the vCenter Server VM

This was originally posted on APC forums on 7/16/2015


Hello,

Environment: PowerChute Virtual Appliance 4.0

I receive the following notice on the PCNS4.0 host protection screen "PowerChute cannot locate the powerchute VM ".  I have seen forum posts regarding powerchute not locating the vCenter Server VM, but not itself.  The vCenter posts indicate a DNS issue. Any recommendations?

I am unsure if this is related but on the same Host protection screen, the Powerchute VM is not identified to be on the correct host.  The host that PCNS believes it to be on is not accurate.  It may have been the host at one point prior to migrating to a different host.   If not related to the above, is there a way to reset/clear the old state?

Thank you

Brennan

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
193

Re: PowerChute cannot locate the vCenter Server VM

This reply was originally posted by Bill on APC forums on 7/16/2015


Hi,

Open vSphere Client, select the PCNS Appliance and click on the summary tab. Does it list the proper host the Appliance is running on? If it does not you should power cycle the VM. If it does you should log into the VM and stop the restart PCNS daemon. The command is service PowerChute stop the service PowerChute start. If neither of those resolves the issue uninstall the Appliance and reinstall it. Before uninstalling the Appliance if you want to save your configuration you should copy pcnsconfig.ini that is in /opt/APC/PowerChute/group1. You can also save EventLog.txt.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
194

Re: PowerChute cannot locate the vCenter Server VM

This reply was originally posted by Bill on APC forums on 7/16/2015


Hi,

Open vSphere Client, select the PCNS Appliance and click on the summary tab. Does it list the proper host the Appliance is running on? If it does not you should power cycle the VM. If it does you should log into the VM and stop the restart PCNS daemon. The command is service PowerChute stop the service PowerChute start. If neither of those resolves the issue uninstall the Appliance and reinstall it. Before uninstalling the Appliance if you want to save your configuration you should copy pcnsconfig.ini that is in /opt/APC/PowerChute/group1. You can also save EventLog.txt.