Power Chute Network Shutdown and Hyper-V Server 2016

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BlackMagic_apc
Crewman
Crewman
0 Likes
5
428

Power Chute Network Shutdown and Hyper-V Server 2016

This was originally posted on APC forums on 4/29/2019


Hi, we're using a mixed VM environment - ESXi and Hyper-V server 2016. I was able to set up ESXi correctly, but I have issues with Hyper-v. What's the actual procedure for the Hyper-V server itself? Should I download "PowerChute Network Shutdown v4.3 for Windows x64" for the Hyper-V and perform bare metal install on the Hyper-V server? Or is there something I'm missing?

Cheers


Accepted Solutions
BlackMagic_apc
Crewman
Crewman
0 Likes
0
431

Re: Power Chute Network Shutdown and Hyper-V Server 2016

This was originally posted on APC forums on 5/6/2019


Problem solved. Firewall issues.

Thank you for your help!

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
430

Re: Power Chute Network Shutdown and Hyper-V Server 2016

This reply was originally posted by Bill on APC forums on 4/29/2019


Hello,

On 4/29/2019 6:03 AM, Oskar said:

Should I download "PowerChute Network Shutdown v4.3 for Windows x64" for the Hyper-V and perform bare metal install on the Hyper-V server?

Yes. You should install on the Hyper-V server and configure for Hyper-V. If using SCVMM you should select that during the configuration process. 

See the PCNS Hyper-V User's Guide for more information.

 

BlackMagic_apc
Crewman
Crewman
0 Likes
0
430

Re: Power Chute Network Shutdown and Hyper-V Server 2016

This was originally posted on APC forums on 4/30/2019


Hello,

The problem is - I'm not able to get to the web configuration panel. Connection times out, doesn't matter if I'm using IP address or name.

Any ideas?

BillP
Administrator Administrator
Administrator
0 Likes
0
431

Re: Power Chute Network Shutdown and Hyper-V Server 2016

This reply was originally posted by Bill on APC forums on 4/30/2019


Hi,

First thing to check is to verify the PCNS service is running. The command is sc query pcns1. If not running you can start the server with the command  sc start pcns1

Next thing to check is to verify that port 6547 is open. The command to check the ports is netstat -a PCNS web interface uses TCP ports 3052 and 6547

 

BlackMagic_apc
Crewman
Crewman
0 Likes
0
431

Re: Power Chute Network Shutdown and Hyper-V Server 2016

This was originally posted on APC forums on 5/6/2019


Hi.

Service is running and ports are good.

Ehh.. Hyper-v is always problematic.
Any other ideas? I'm kinda stuck here and I'd love to finish our UPS setup.

Cheers!

BlackMagic_apc
Crewman
Crewman
0 Likes
0
432

Re: Power Chute Network Shutdown and Hyper-V Server 2016

This was originally posted on APC forums on 5/6/2019


Problem solved. Firewall issues.

Thank you for your help!