PDU Metering low power devices and standby state.

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
testronic-bert_apc
Cadet
0 Likes
5
185

PDU Metering low power devices and standby state.

This was originally posted on APC forums on 5/21/2013


Hi,

We are installing a metered by outlet PDU (AP8653) in a test setup.
Our goal was to detect standby states in low power test devices, but it turns out that I can't even tell if the device is on.

I have a device on outlet 1, but the outlet status page says 0 for all 3 columns (state == ON)


The devices use at least 10W when running. When they're in standby mode that goes down to 1W or less.

Is there a possible solution to have a more precise reading?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
185

Re: PDU Metering low power devices and standby state.

This reply was originally posted by Angela on APC forums on 5/21/2013


We can accommodate maybe a little lower than 0.5A (say 0.3A) on special requests but that is as low as we can go and remain relatively accurate.

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
187

Re: PDU Metering low power devices and standby state.

This reply was originally posted by Angela on APC forums on 5/21/2013


Our accuracy information for these PDUs is located in the knowledge base (http://www.apc.com/site/support/index.cfm/faq/) in article ID FA156074

Can you let me know what accuracy readings you are looking for in Amps?

testronic-bert_apc
Cadet
0 Likes
0
187

Re: PDU Metering low power devices and standby state.

This was originally posted on APC forums on 5/21/2013


I see the minimal Amps is 0.5A for a reading for it to show.
We would need a minimum of 0.05A to know if the device is on.

BillP
Administrator Administrator
Administrator
0 Likes
0
187

Re: PDU Metering low power devices and standby state.

This reply was originally posted by Angela on APC forums on 5/21/2013


Yes, we cannot go that low unfortunately..

testronic-bert_apc
Cadet
0 Likes
0
187

Re: PDU Metering low power devices and standby state.

This was originally posted on APC forums on 5/21/2013


That's unfortunate. It makes the 8 PDUs as usefull as the €50 remote accessable powerstrips we have.
They just look more shiny.

I couldn't even see the tv I hooked up to test it!

If a lower reading is less accurate, so be it, but not seeing anything at all renders the PDUs mostly useless.
That info would have been usefull back in October when we ordered them.

BillP
Administrator Administrator
Administrator
0 Likes
0
186

Re: PDU Metering low power devices and standby state.

This reply was originally posted by Angela on APC forums on 5/21/2013


We can accommodate maybe a little lower than 0.5A (say 0.3A) on special requests but that is as low as we can go and remain relatively accurate.